Answer / hammad khan (university of wes
Not Necessary, Like in Siemens Siprotec Relay we can change the CT star point. There are two options, towards the time or towards the busbar. So however your CT star point is in the field you can configure it in the relay.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / hammad khan (university of wes
In the above post, its towards the Line or towards the Busbar,
sorry about the typo.
| Is This Answer Correct ? | 2 Yes | 1 No |
What are the factors to be considered during the Synchronization?
What is different between resistance grounding system and resistance earthing system?
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
What is the difference between line Distance protection and Line Earth Fault Protection?
Why converter duty transformer neutrals are not earthed...i am still not sure if this question is also correct...Please email at ranjan120482@gmail.com
what is the differance between HT motors And LT MOTORS.
0 Answers Empire Vitrum Glass, Sappi,
I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency 75%(star delta connection)Motor. How to calculate line current & Phase current (1) Star connection (2) delta Connection
I need to connect a synchronous generator to the grid using automatic synchronization and two circuit breakers (one for synchronization, one for end connection to the grid), how to determinate the required diameter of the cables?
WHAT IS MOBILE SUB-STATION? & REALLY BENEFIT IN INDIA
how oltc works in rectiformers of higher rating (27 mva,200v dc,120kamps) please provide me full information with diaggram.
haw to calculate resistance of induction motar
what is LUX?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)