Current Transformer's star point must face the protected
object for the relay operation?
Answers were Sorted based on User's Feedback
Answer / hammad khan (university of wes
Not Necessary, Like in Siemens Siprotec Relay we can change the CT star point. There are two options, towards the time or towards the busbar. So however your CT star point is in the field you can configure it in the relay.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / hammad khan (university of wes
In the above post, its towards the Line or towards the Busbar,
sorry about the typo.
Is This Answer Correct ? | 2 Yes | 1 No |
What is the automatic voltage regulator with servomotor?
howmany electrician should maintain for a 1000 kva used plant... in kerala..
for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?
how calculate kva in to kw
Can anyone tell me how a 12v battery is transformed to 20,000v at the spark plug
what is the difference beteen differential protection and over current protection of an alternator
WHY LINK NOT A FUSE IN AC CIRCUIT
For 132 KV line, PT or CVT which is prefered for measuring & protection? is there any IS or IEE standard available?
I WANT YHE TECHNICAL AND ELECTRICAL SPECIFICATIONS OF 2x4MW 11KV 2x10MW 11KV 2x25MW 11KV 2x100MW 11KV HYDEL POWER PLANT i.e PROTECTION SYSTEM,MONITORING,CONTROL SYSTEM,GENERATION,SYNCHRONISATION,METERING PLEASE SEND THE DETAILS TO MY MAIL ID SPRAVEEN_222@YAHOO.CO.IN
What is the operating range of voltage and current in grid supply in India?
why rating of generator is kva but motor is kw ?
what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY