Any one Give me formula for to increse the power factor,
0.8 to 0.95, How much the KVAr Required
Answer Posted / sonam sherpa
P.F = M.D*(Tan(cos-1 x)-Tan(cos-1 y))
M.D - max. demand.
x- Actual power factor
y- Required power factor
| Is This Answer Correct ? | 4 Yes | 0 No |
Post New Answer View All Answers