How will you calaculate the Ct ratio based on connected
load 500KVA,and 11KV supply ?
Answers were Sorted based on User's Feedback
Answer / venu
p=root3*v*i
500K=root3*11K*I
hence we get
I=62.096
so this is the maximum current flowing to the particular
load so we can use 75/1A ratio CT
| Is This Answer Correct ? | 19 Yes | 9 No |
Answer / pkv
50/5 or 50/5 depending upon the protection relay amp
| Is This Answer Correct ? | 3 Yes | 1 No |
what are safety seals in HT line?
what is the ranje of HT cabel and LT Cabel.
what are the alternator cooling system? how it is represented?
what is the concept of star delta starter?
what is mean by hormonics & surge? and it's effects?
how to calculate capacitor bank value to maintain unity power factor plz xplain with some suitable xample?
which braking is used in traction motor and what is its working send at mukeskumar27@hotmail.com
we touch other end of the tester supply, why do not get shock?
What are the tests to be conducted in the electrical installations
sometimes, eventhough the HV side of the transformer is opened there is a voltage in LV side .How is it possible?
What is the difference between neutral and ground?
3 Answers Cethar Limited, Torrent Power,
what is need of air gap in expansion section in busbar?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)