How will you calaculate the Ct ratio based on connected
load 500KVA,and 11KV supply ?
Answers were Sorted based on User's Feedback
Answer / venu
p=root3*v*i
500K=root3*11K*I
hence we get
I=62.096
so this is the maximum current flowing to the particular
load so we can use 75/1A ratio CT
Is This Answer Correct ? | 19 Yes | 9 No |
Answer / pkv
50/5 or 50/5 depending upon the protection relay amp
Is This Answer Correct ? | 3 Yes | 1 No |
What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?
What are the basic elements used for modeling mechanical rotational system?
Most electrical terms denoted by first letter of its name but Why current is denoted by "I".
who many types of fire explane with exmple
what is function of centrifugal switch in single phase induction motor..?
How does the phase sequence controller works, how it identifies the phases? confirm working principle
1) Can anyone give me a typical value for Insulation Resistance of 11kV xlpe cable? 2) How much will the IR value decrease per KM of cable length added?
I want to ask that is there any relation between current denesity of copper and material purity. also is ther any standard which defines the standard current denesity of material.
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side
What is error of a measurement?
what is current actully?significance of current...not rate of change of flow.....
what are symmetrical and non symmetrical components in electrical installation.