how to calculate capacitor bank value to maintain unity
power factor plz xplain with some suitable xample?
Answers were Sorted based on User's Feedback
Answer / er. ankush miglani 9718151073
KVAR= KW(TAN(COS(-1)#e)- TAN(COS(-1)#d) )
#e= EXISTING P.F.
#d= DESIRED P.F.
Is This Answer Correct ? | 35 Yes | 3 No |
Answer / shalini.b
capacitor bank value is calculated in KVAR
From Power Triangle,
KVAR = Sin(phi) * KVA
Desired Power factor = 0.96 (say)
cos(phi)=0.96
phi = cos(inv)0.96
phi= 36.86
Sin(phi)= 0.28
If the transformer rating is 1250 KVA (say)
KVAR = 0.28*1250
= 350
Is This Answer Correct ? | 22 Yes | 8 No |
Answer / maen drawish
The proper calculation for cap. bank it depends on the
desired & initial/ existing cos-phi.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / skumar
I don't know the correct formula. But in practical we
applying 30% of our full load(i.e transformer capacity).
Is This Answer Correct ? | 4 Yes | 7 No |
why the transformer primary and secondary windins vector groups vary? why it is something like Dy11 and not as Dy or Yy...
why can't we provide dc supply to a transformer?
Why does the rotor rotate?
when the flux enters into saturation mode then what will be the secondary voltage of the normal t/f?....high or low ? explain ...how?
why we +ve load distribution in 24v and -ve load distribution in 48volt in the telecom sector.?
if there are six generators (3 gas CATT, one Jenbacher o1 MW each, and two nos Diesel 01 no 01 mw other 0.65mw EDGs ( say), 3 CAtt gas set have identical pole pitch,01mw EDG and Jenbacher gas Set have different pole pitch, how their power connection can be done to connect a common bus bar during installation. in short, how different pole pitched generators power connection can be done to connect a common busbar system through generators incomer ACBs.
What is steady state response?
What is the technical reason for adopting color coding of three phase system as RYB.
what is the total power generation in india?
explain all the classes with example
A power transformer 4MVA/11KV/0.415Kv has been out of use in 12years. what maintenance actions/test need to be carried out before energizing.
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test. why transformer rating in always in KVA ? what ispositive, negative, zero sequence impedence? How ElCB tripping if Neutral touch with ground Why AC & DC capacitor are use in UPS ? why motor rating in KW? how to syncronize two dg sets