how to calculate capacitor bank value to maintain unity
power factor plz xplain with some suitable xample?
Answers were Sorted based on User's Feedback
Answer / er. ankush miglani 9718151073
KVAR= KW(TAN(COS(-1)#e)- TAN(COS(-1)#d) )
#e= EXISTING P.F.
#d= DESIRED P.F.
| Is This Answer Correct ? | 35 Yes | 3 No |
Answer / shalini.b
capacitor bank value is calculated in KVAR
From Power Triangle,
KVAR = Sin(phi) * KVA
Desired Power factor = 0.96 (say)
cos(phi)=0.96
phi = cos(inv)0.96
phi= 36.86
Sin(phi)= 0.28
If the transformer rating is 1250 KVA (say)
KVAR = 0.28*1250
= 350
| Is This Answer Correct ? | 22 Yes | 8 No |
Answer / maen drawish
The proper calculation for cap. bank it depends on the
desired & initial/ existing cos-phi.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / skumar
I don't know the correct formula. But in practical we
applying 30% of our full load(i.e transformer capacity).
| Is This Answer Correct ? | 4 Yes | 7 No |
Stator of 3-phase IM has 3 slots per pole per phase. If supply frequency is 50 Hz, calculate the speed of rotating stator flux A 1000 rpm B 500 rpm C 1500 rpm D 1440 rpm
slipring induction motor starting time Lrs operating why lrs starting time lrs outer body didn't get shock
(1)WHAT HAPPENS WHEN SUDDENLY LOAD GIVEN TO THE INDUCTION MOTOR ? (2)CAN WE MAKE WOOD AS MAGNET ? (3)WHAT IS THE VALUE OF MAGNETIC FLUX DENSITY IN TRANSFORMER ? (4)WHY WE ARE USING ELECTROMAGNETI NOT ELECTROSTATIC IN MACHINE ?
what are the applications of PLC?
1 tr is equal to how many Kw .is there any specific formula for this to get the result .
13 Answers Cipla, LG, NSN,
simple way to find busbar sizes??
why fractional pitch winding generally used in alternators?
what is mean by flux
Hello friends, Can anyone explain the concept of zones in Bus bar protection and how can we differentiate the main zone and check zone in Bus bar protection
1600 KVA ka transformer hi aghar lt side par 800A aur voltage 420 ho to HT side ki cable ki rating keya ho gi?
why do fans generally rotate in anti clock wise direction??
If any HVDC line is going with positive & negative(the negative usually have return path of current with earthing electrode). Now the question is if this HVDC earthed electrode which is using as return path and earthed any nearby 400kv or 220kv AC substation equipments. which will be the impact of this on AC substation & its equipment, how severe may be this and what should be the minimum distance require between HVDC earthed electrode and AC substation equipments? It's really an high engineering level question...Dare to answer and increase your knowledge.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)