What are ampers.30kw motor.440volts.
Answers were Sorted based on User's Feedback
Answer / abo ibrahim
Active Power=1.732*Load Current*Line Voltage*P.F.
P.F=0.8.
Active Power= 30kw = 3o*1000= 30000w
Load Current= 30000\(1.732*440*0.8).
=49.21 Amp.
| Is This Answer Correct ? | 16 Yes | 1 No |
Answer / elangkumanan
1kw= 1000watt
power =1.732*440*I*0.80
KW*1000
= ----------------
1.732*440*I*0.80
30*1000
= -----------------
609.664
30000
= ------- 49.20A THAT IS ANSWER FOR THIS QUESTION
609.664
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / d v singh
30*1.35*746
--------------
1.732*440*.95*.85
30213
---------------
621.85
= 48.58 AMP
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / pinoy
P=1.732 X LINE VOLTGE X I ; NO NEED TO MULTIPLY BY P.F
SINCE POWER (KW) IS KNOWN HENCE,ONLY MULTIPLY BY P.F IF
P=KVA
I=30KW/1.732(440)
=39.37AMPERES,
| Is This Answer Correct ? | 1 Yes | 1 No |
Can we use same copper cable for both AC & DC power.
1 “earthing” for bonding of equipment and circuits to common plant earth electrode potential, 2 “protective earthing (PE)” when this bonding is required for personal safety provisions 3 “grounding” for interference suppressing bonding of screens, sys-tems with ground level 4. low-impedance earthing ? 5.primary earthing system and secondary earthing system what is that? 6.earthing electrode or mesh net earthing electrode ? very confusing , simple but very informative help required ? i will be very very thankful to you guys.
What are the protection schemes used for protection of transformers ?
3 Answers Engineers India Limited,
What is the formulae of Megger value for a A.C.Motor
what is impedence voltage
why we used servo motor insted of inducation motor?
what is the problem with single phase AC motors and how is it overcome?
What are various accuracy classes of CT(Current Transformer)
Can anybody suggest me about what are all the TECHNICAL CERTIFICATIONS avilable for Electrical Engineers for working people with clear details??
how to get electrical supervisour certificate in gujarat
Why do we use 36KV LAS for 33kv line and 9KV LAS for 11KV line?
What iz main protection of mediuum voltage motors and what iz the standard IR voltage of 6.6 and 11kv motors.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)