How would you supply a single house hold load from a 3-phase
supply coming out of a sub-station?
Answers were Sorted based on User's Feedback
3-phase supply from a sub-station will be 11kv or
6.6kv.This Voltage is stepped down to 440V by the
distribution Transformer,the distribution transformer has
Delta - Star connection, so in the output side you will hav
neutral line.
Now the phase voltage is 440 V.To supply house hold load we
connect the mains between a phase and neutral
Is This Answer Correct ? | 62 Yes | 1 No |
Answer / naresh desetti
to use a 11kv by 440 step down t/f after we will get a 440 volts with neutral point
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / gopal manda
for only a single house hold load we dont establish three
phase sub station,we establish sigle phase transformer
(5kva,10kva) according to load.for the primary input we
input phase voltage 6.6 kv,one terminal of primary connect
to 11kv phase and other is grounded which is neutral.and we
get 230 volt at secondary.
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / fireprs
step down 3-phase supply using step down transformer upto
440 V,then can be used by making scott connection,or by
using it through a diffrent neutral or if it is delta-star
connnected use the neutral of secondary.
Is This Answer Correct ? | 3 Yes | 11 No |
what is the surge arrestor?how it operates?what is the range for it?
if vcb make contact but output notreach give the reason?
What is the function of semicon in 33kv ht cable ?
How can we calculate the Rating of DG Set for a 4 kw motor?
we all know that in transformer, voltage and current are inversely related i.e. Vp/Vs= Is/Ip....so in standard CT..we have a ratio of 200/5...that means our voltage should increase by ratio of 40..althoug that is not the case...because that requires high insulation level.and pratically not feasible......can anybody clarify my ques.......thanx
What is the function of auadag in a cro?
what is the use of reactive power
How can we calculate strength of copper hich is supplying electric power to heater and in it hold the heater also and what r all types of forces which is acting on it...
What is the difference between earthed & unearthed system?
hot water tank,top element 240v across,the bottom 120v across,why?
Will an earth leakage trip be activated if the component or wiring is faulty on low voltage equipment.Example An electrical Cat Scarer placed in the garden and water gets into the wiring.
hi frnds.....anyone get any reply from HPCL. I HAVN'T.....B,COS written will b on FEB 17 th.