For polarity test on a 11/3.3kV 2.5MVA delta-star Unit
Auxiliary transformer,415V 3-phase supply was applied at
the HV. Connection between Aa was made with a 2.5mm cable.
As soon as power was switched on the cable caught fire and
burnt. This test was then abandoned. It is noteworthy to
say that a similar cable was also used in a similar
transformer for the same. The cable did not burn and test
was successfully completed with good result. What is wrong?
Please, help me out.
Answers were Sorted based on User's Feedback
Answer / jatinder singh
Please do the megger testing of HV winding.May be the
winding was short circuited.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gurucharan singh
When cable burnt, it is clear that there was over current
in the 2.5mm2 cable. That means load connected may faulty,
or oversize then the capacity of 2.5mm2 cable current
carrying.
| Is This Answer Correct ? | 1 Yes | 1 No |
Thanks to the respondent.I would like to tell him that no
load was connected besides linking Aa in accordance with
the method for the test. Also, note that similar 2.5mm2
cable has been used on a similar Unit Auxiliary 2.5MVA
11/3.3kV delta-star T/F and 60MVA 132/11kV star-delta T/F
respectively. No burning occurred. Test results were
satisfactory. This piece of information should guide any
contributor. Thanks.
| Is This Answer Correct ? | 0 Yes | 0 No |
What are the differences between single phase and three phase?
george phenomenon of synchronous machine
Hi everyone, I'm Lachuu, recently joined automation company as PLC Engineer. I have certain basic question, I request all big gurus and seniors to answer these question. Because this will be very helpful to me as well starters like me. How to design a control circuit (ex: pick & place - my current project) Yamaha robot PxYx series controller RCX222, using 6 cylinder double acting, plc keyence kv p16r 2 expansion unit for input and output each. How to select panel terminal mcb elcb powersupply. My main concern in some projects how to select dc power supply, mcb rcb(I came across dif bt b c d curves, but stil confusing, pls help me :-(. I would really appreciate all who are going respond to this question.
what will be the efficiency off x'mer during no load test and during short circuit test
1 Answers GPSC Gujarat Public Service Commission,
what type of relay has to be used for tripping the circuit from mains when a fault occur in a machine
What is “pu” in electrical engineering?
what kind of motor is used for lifting applications
What is the reason of using bus-bars on the secondary on the LT transformers?
ohms law aplicable
What is the high tension lines voltage and low tension lines voltage?33 kv is high tension line or low tension.
can any one list the class-a, class-b & class-c trips of power generator?
can we charge 3 ph power transformer delta-star wound with neutral grounded 6.6kV/415V from secondary side(415V) but with primary(6.6kV) open by dg,what are the disadvantages or losses.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)