For polarity test on a 11/3.3kV 2.5MVA delta-star Unit
Auxiliary transformer,415V 3-phase supply was applied at
the HV. Connection between Aa was made with a 2.5mm cable.
As soon as power was switched on the cable caught fire and
burnt. This test was then abandoned. It is noteworthy to
say that a similar cable was also used in a similar
transformer for the same. The cable did not burn and test
was successfully completed with good result. What is wrong?
Please, help me out.
Answers were Sorted based on User's Feedback
Answer / jatinder singh
Please do the megger testing of HV winding.May be the
winding was short circuited.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / gurucharan singh
When cable burnt, it is clear that there was over current
in the 2.5mm2 cable. That means load connected may faulty,
or oversize then the capacity of 2.5mm2 cable current
carrying.
| Is This Answer Correct ? | 1 Yes | 1 No |
Thanks to the respondent.I would like to tell him that no
load was connected besides linking Aa in accordance with
the method for the test. Also, note that similar 2.5mm2
cable has been used on a similar Unit Auxiliary 2.5MVA
11/3.3kV delta-star T/F and 60MVA 132/11kV star-delta T/F
respectively. No burning occurred. Test results were
satisfactory. This piece of information should guide any
contributor. Thanks.
| Is This Answer Correct ? | 0 Yes | 0 No |
from which formula we select a capacitor rating?
what is fundamental difference between voltage and current
why are transformers rated in KVA and not in KW
How can you calculate in detail the VA burden of current transformer used for Restricted earth fault protection? Please understand that the CT required here is Class PX or X. Also please show the calculations for knee point vtg, stabilizing resistor, magnetising current.
i am going to attaned the engineer (disign)iterview at HAL please give me duid line
What is Energy Audit..?
why odd hormonics only will effect the power system.why not even hormonics
what is the suitable voltage of transmission line to transmit 10000w power through 250 km. (a)11kv (b)33kv (c)66kv (d)132kv ]and please tell me whats the logic behind it
why breaker closing coil gets burnt if supply is continously provided to it.
how we calculate size of exciter(excit. volt and current) for generator?
Why current transformer is earthed??
Define availability (operational)?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)