what is difference between tension tower and suspension
tower?
Answers were Sorted based on User's Feedback
Answer / eng_entropy
For tension tower:-
It located between every three or four suspension tower to
pull the conductors which are re-tied in tension tower
insulators.
For suspension tower:-
The conductors just hung-up on it's insulators and not to
re-tied on it (I mean it just pass through a ring at the
end of the insulator).
| Is This Answer Correct ? | 38 Yes | 12 No |
Answer / pankaj singh khetwal
when routing of tower deviates an angle more than 2 degrees
then tower at point of deviation faces tension due to pull
in conductors and hence known as tension tower where as
tower with angle is less than 2 degrees line deviation is
known as suspension tower
| Is This Answer Correct ? | 16 Yes | 3 No |
Answer / vaidy
The tension tower carries both horizontal and vertical load.
The supporting tower carries only vertical loads.
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / malik
tension tower = (Road crossing,deviation in transmission
line )wr conductor is tied up firmly by means of tension
insulator
suspension tower = to minimize the sag the conductor s just
tied up with suspension insulators
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / dipanku goswami
Suspension tower is used where the angle of deviation of the TL route is 0-2 degrees. Here the conductor is simply suspended on the insulators.
where as tension towers (B,C,D type) are used where angle of deviationof the TL route vary from 2-60 degrees.Strain type insulators are usedc in this case.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / gunasekaran
if u use insulator as a suspension type that is suspension
tower.use as a strain type that is tension tower. in strin
type sag is less than suspension.
| Is This Answer Correct ? | 7 Yes | 10 No |
Answer / simhachalam
Tension is above 90kn
Suspension is below 90kn
MS CHALAM(GOLDSTONE)
| Is This Answer Correct ? | 5 Yes | 12 No |
why induction motor's p.f 0.8
If not maintained 3 phase clearance,what happened ?
What is Instantaneous Earth fault relay,how will work
why power factor occur only inductive load not in resistive ?
How to calculate load requirement of a 50 flat apartment with 5 kw each unit,sizing of cable,transformer
what is the different between Switch & Circuit Breaker?
if we supply to secondary winding how transformer work?
How can we calculate the fault level of the distribution system knowing the percentage impedance of transformer & subsequent equipments.
What is a HRC fuse (Full form)
26 Answers Gammon, HRC, Moser Baer,
What is difference between ON delay and OFF Delay Timer?
5- What is the task (function) of the excitation and isolation transformers in power plant? 6- What is the task (function) of LCI (A), LCI (B) and LCI (COS) in power plant? : LCI (A) and LCI(B) are load commutating inverter for generator turbine starting. , LCI (COS) is load commutating inverter change over switch
where we use compound motors in real time and why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)