what is the formula to calculate kva genset required for a
given load in kw.
Answers were Sorted based on User's Feedback
Kva Required is = KW/0.8( Power factor )
& as the DG set is prefered to run at 80% load of the total
capacity then the Rated capacity is KVA/0.8
If the load is 100 KW rhen KVa is 100/0.8 = 125 KVa & the
rated kva is 125/0.8 = 156.25 KVA say 160 kva D.G set is
required.
Is This Answer Correct ? | 34 Yes | 6 No |
Answer / vaibhav kr. pathak (ongc,hazir
Normaly relation between kVA and kW can be described as:
For 1phase system->kW=kVA X power factor.
For 3phase system->kW=3^(1/2)*V*I*power factor (V&I are
line voltage and current respectively)
Is This Answer Correct ? | 3 Yes | 0 No |
how to convert kw in to unit
there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit
what is IP55,IP65
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
What is formula calculation size cable wire ?
What is the difference of grounding and earthing?
what is necessity of using isolation transformer?
Why not connect relay Y phase for over current and earth fault
What is slip in induction motor?
what is dead tank CT AND what is live tank CT
How to control motor gearbox speed and friquency? If length of cable and dia given, how to measure the voltage drop?
What it is the diff btw Package & PEC AC's????