will we have to design the UPS differently for both i.e. if
we want to connect the two batteries in parallel and/or we
want to connect the two batteries in series ?
Answers were Sorted based on User's Feedback
Answer / aamod tripathi
OBVIOUSLY THE AMPERE HOUR CAPACITY AND THE INPUT VOLTAGE TO
THE UPS WILL BE DIFFERENT IN BOTH THE CASES THUS U WILL
HAVE TO DESIGN DIFFERENTLY FOR BOTH
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / imran
In series the input voltage to ups increase and in parller
ampher hour capacity got double e.g i have two battery of
rating 12v 18ah . In parlel i get 12v 36ah and in series i
get 24v 18ah
| Is This Answer Correct ? | 2 Yes | 0 No |
which has the Ampere hour capacity greater
& which has the input voltage greater
& what would be the difference in designing the both UPS ?
thanks
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kiran s.
You connect both battery in parallel so it will be theoretically and practically right
| Is This Answer Correct ? | 0 Yes | 0 No |
my question is that....few days ago i had installed a three phase motor starter for an electric saw.the motor will run and make the hydraulic pressure which will be goes to pressure cylender by up and down lever.two number of limitswitches are also installed on cylinder for safety of motor.now when the arm of cylinder reaches to the upper or lower limit it will cut the motor's line.and motor will be stop.now wana know that what will i do that motor runs continue after the limitswitch cut it down but it shold not be made any pressure.pls answer me in brief.
what is purpose of using neutral grounding transformer in generators??
800A 22KV TP OCB. explain
Is it benefitial to supply 210v ac to lighting fixtures instead of 240v ac?
how can i use REF and diffrencial relay both in 1 CT core for transformer protection?
How capacitor improves pf
What is formula of capacitor for 1-phase power connection.how to improve PF. Suppose I want to connect capacitor in refrigerator to reduce power consumptions.
What are the different protection systems used to protect the transformer internally and externally?
What is the actual calculation for transformer short circuit test?.
WHAT IS M.P.C.B
How to calculate no of Lighning arrestors are required for protecting 50mX 50m*20m cubical building and locations of LA?
how synchronous condenser is used in place of synchronous generator with out negotiating IEEE standards? Can i use 3 generators as synchronous generators and 2 generators as a synchronous condensers in an IEEE 14 bus system with out disturbing the standards?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)