will we have to design the UPS differently for both i.e. if
we want to connect the two batteries in parallel and/or we
want to connect the two batteries in series ?
Answers were Sorted based on User's Feedback
Answer / aamod tripathi
OBVIOUSLY THE AMPERE HOUR CAPACITY AND THE INPUT VOLTAGE TO
THE UPS WILL BE DIFFERENT IN BOTH THE CASES THUS U WILL
HAVE TO DESIGN DIFFERENTLY FOR BOTH
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / imran
In series the input voltage to ups increase and in parller
ampher hour capacity got double e.g i have two battery of
rating 12v 18ah . In parlel i get 12v 36ah and in series i
get 24v 18ah
| Is This Answer Correct ? | 2 Yes | 0 No |
which has the Ampere hour capacity greater
& which has the input voltage greater
& what would be the difference in designing the both UPS ?
thanks
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kiran s.
You connect both battery in parallel so it will be theoretically and practically right
| Is This Answer Correct ? | 0 Yes | 0 No |
what is spadar bar .why I use in DC generator.
Stepwise process of Northern grid failure in 2012!? (dont copy paste from wikipedia)
1 Answers Rashtriya Ispat Nigam Limited RINL,
What do you mean by ratio correction factor of instrument transformer?
how calculate cable size in squre mm, when the load is given by in kw? do u have current rating chart of elctrical cables?
Anybody tell me about modbus hex address of l&t trivector meter er300p??I want to read voltage,current,kwh etc via rs485...If anybody have a manual then send on my mail..Brijeshmodi18@gmail.Com
what is different between earthing and grounding for a electrical eqipment ?
2 Answers BARC, Omega Maritime,
Define open loop control system.
Define working of prim mover governer in alternator?
why it is mentioned as 8/10 mva transformer why not directly 8mva or 10mva transformer. please explain me the full detailed reason.
To prove the capacity of a 10MVA transforemr with 6.5% impedance by a short circuit test how much power is needed to inject an impedance voltage if we have to arrive for its rated current?
when 20hp 3 phase motor start no load condition in star or delta connection.find current and write formula.(tariq)
Difference between divercity and power factor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)