Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to make a calliberation for deffirential pressure

Answers were Sorted based on User's Feedback



how to make a calliberation for deffirential pressure..

Answer / s

When Differential pressure gauge or Transmitter put in open
to atmosphere condition,adjust zero.Apply Maximum Pressure
at HP side and Adjust span by adjusting link in the case of
Diff.Preesure gauge or adjusting span screw in case of
analog Diff.Pr.Transmitter.

Is This Answer Correct ?    5 Yes 0 No

how to make a calliberation for deffirential pressure..

Answer / vinesh prajapati

When Differential pressure gauge or Transmitter(H.P.
SIDE,L.P. SIDE parellal) put in open
to atmosphere condition,adjust zero.Apply Maximum Pressure
at HP side and Adjust span by adjusting link in the case of
Diff.Preesure gauge or adjusting span screw in case of
analog Diff.Pr.Transmitter.

Is This Answer Correct ?    2 Yes 0 No

how to make a calliberation for deffirential pressure..

Answer / haridass

DP Transmitter are used in the measurement of level/flow
measurement/DP of filters.. Here both the lp & hp points
are rather important.

To calibrate the transmitter:

confirm the cell and adapter blocks are clear,

Apply both side the equal pressure by opening the equalizer
valve (Less than its MWP-max working pressure),
should be 4 mA. (This is called Static test)

Make zero trim if found error.

Apply the required range of pressure, only in hp side and
zdj to 20 mA. Again chk 0%, if error found adj zero. After
no error found in zero/span then proceed next step.

Apply pressure and note 4-5 points of its range in hp
side., increasing and decreasing (to avoid hystersis error).

Make write protect and calibration tag on transmitter.

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

In closed loop control there are several “blocks” used to show the interactions between the process and the control system. These blocks are referred to as the “process” and the “controller.” Describe the relationship between these two blocks when creating a well tuned control loop.

1 Answers  


please tell me five types of fault of control valve and positioners?please

1 Answers  


what is upstream and downstream in liquid flow?

6 Answers   Thermax,


How does milli volt is created in themocouple?

2 Answers   Jaypee,


whatis virtual instrumention?

5 Answers  


whats the diff b/w zero pressure and obsolute pressure

4 Answers  


how to change 4 wire rtd transmitter into a 3 wire rtd transmitter? as our transmitter is working for 4 wire rtd, what should do for working on 3 wire rtd transmitter

1 Answers   HHJ,


what is function of DCS , and how is it work , explain with difination

1 Answers   Bapco Bahrain Petroleum Company,


what is the difference between PLC & DCS

17 Answers   L&T,


Tell me about the synchronization panel.

1 Answers  


when an eddy current probe is installed inside of a turbine or compressor in case of probe problem same as:crash of head of probe,changing the scale factor because of low measuring gap(physical gap is ok(example=1.14mm)but voltage is reduced(example=-6 volts),is any way to check the probe,when the ohm of probe is ok.thank you,(Karim Tavakoli)

1 Answers  


How many input(Analog and digital) and outputs(Analog and digital) are there in DELTA v DCS Version 7.0?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)