how to measure the output of RTD given the general formula of rtd.
Answers were Sorted based on User's Feedback
RTD's output is resistance.
As we know RTD means resistance temperature detector, so we measure resistance across the terminal of RTD by multimeter.
Now assume measured resistance is "X" and RTD we are using is PT100 then,
T(temp)=(X-100)/(0.386)
*PT100 RTD shows 100 ohm at 0°c
| Is This Answer Correct ? | 17 Yes | 0 No |
Answer / rajesh.
RTD is Resistance Temperature Detector. As temperature varies resistance also change. So the output of RTD is Resistance. Which in terms converted into current (4 – 20 ma) by means of Transmitter. Generally RTD is available as Pt100.
Pt100 means 100OHMS at 0’ C for a platinum resistance bulb.
Formula for RTD:
Rt. =Ro (1+α t)
Rt. =Resistance of zero temperature.
α = Co. off of thermal (expansion)
t = temperature to be measured.
Example:
Calculation of Resistance or Pt 100.
Ro. = 100
α for platinum = 0.00385/c.
To calculate Resistance at 100’c
R100 =100(1+(38.5*104*100))
100+ (100*0.385)
R100 =138.5
Resistance at 100’c = 138.5
| Is This Answer Correct ? | 4 Yes | 0 No |
I m appointed as an automation trainee engineer in small firm in that I am only the one , my company give me a project on s7-200 as i m beginner I don't know how to program so please send me the helpful site so that I complete my project before deadline....please help me out in this critical situation.
what is compensation? temprature & pressure
why we use 4-20 mA for calibration of the instruments.why we cant use 0-20 mA?
why pressure 3-15psi is used as industrial standard and what is the reason
2 Answers JAL International, UltraTech,
What is the deffernce bet. Instrumentation and Electrical Enginerring?
why used three wire in RTD.
How much voltage we are using at switches?
In most process, speed of motor controlled by control system with a reference pot . Now if i start & it becomes uncontrollable, i.e.gets directly start & stop after certain time.Then which reasons can make such problem? can motor may be faulty?how?
In RTU Panel we are having several Analogue & Digital Inputs /Outputs. We are recently facing some problems over Analog inputs , which are not updating properly (But Digital Input are updating normally) Can any one tell me from where the problem is creating , we have checked PLC CPU card, Analog Input card & we reconfigured ,But still the issue is there. Issue : 1. Sometimes Analog values are updating & sometimes not. 2. Analog values are not updating normally , showing some wrong Values 3. Total dead (0 value) Analog values are Level & flow measurement from the field instruments. (But in field the instruments are working normally & Displaying the values normally in local display unit) This problem we are facing in our Water Plant. If any one experienced this same problem or having any ideas related to our issue PLS send your valuable Answers/Replies...
how to check the leak in thermowells
hay friends, i am in trouble to understand PID controller. several times i have study but it is not clear to me have you a simple way to understand.
what is modbus & what signals are taken through it
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)