Answer / e venkat reddy
if u apply DC voltage to transformer,
reactive load whose formula is
Xl=2*phi*f*L
In pure dc the frequency is zero so inductive reactance is
zero and the resistance of transformer is very small ie .2
to .4 ohms. if u apply 230v DC then the current will be
230/.4= 575 amps so that it is going to burn winding of the
transformer. so we use transformer only for AC voltage.
| Is This Answer Correct ? | 14 Yes | 0 No |
Answer / glen saldanha
it depend whether it is dc pulsating or pure dc waveform
as transformer is a reacive load whose formula is
Xl=2phi f L
In pure dc the frequency is zero so it is as good as a
short circuit but in case of pulsating dc as frequency is
known it will definately produce a dc pulsating at the
secondary of the transformer output.Example in SMPS of your
computer these transformer are used.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / ranjith
The principle involved in working of a transformer is
mutual induction. Both electrical and magnetic energy are
interchangeable.
Simply saying change in magnetic field creates emf.
i.e., if flux linking with a coil changes due to the
current flowing in the same coil, then the type of emf
induced is called self induce emf.
Similarly if the flux linking with the coil is changing due
to the current flowing in another coil, then the type of
emf induced is called mutually induce emf. This is the
principle involved in transformer.
The transformer has two windings namely low voltage (L.V)
and high voltage (H.V). These two coils (windings)
magnetically coupled but electrically isolated. The
connection between these two coils existing when there is a
change in flux which is only set up by AC. This is not the
case in that of DC.
Dc means no change in flux-> no emf -> no coupling between
two coils.
So the winding which we give supply is just seems to be
short circuited. So if the resistance is not capable to
oppose the current-> high current-> coil burns.
What will happen if I apply DC to AC transformer?
Theoretically not works
But practically the transformer will burn. It may be
varying for rating of the transformer also.
Transformer means it is for ac only
No need to say it as ac transformer.
| Is This Answer Correct ? | 9 Yes | 2 No |
Short Answer: Nothing will happen
Long Answer: Transformer reacts in AC since the working principle is induction by primary coil to the secondary coil (giving step-up or step down VOLTAGE, depending on number of coil turns in them)
This induction happens if you have rate of change in voltage i.e AC, or at the start of your termination of your DC (from 0V to whatever your DC voltage).
Therefore, in your case, the transformer will act as a transformer only at the beginning of the DC connection (well, think: when you disconnect also...)
During steady state when the DC has stabilized, nothing will happen because there's no rate of change in voltage anymore.
| Is This Answer Correct ? | 4 Yes | 4 No |
The maximum demand of consumer is 2 kW and his daily energy consumption is 20 units. Its Load Factor is (1) 10.15% (2) 41.6 % (3) 50 % (4) 60%
synchronous motor of 13.5MW having which type protection? and how to set relay?give me relay setting calculation for different protection for this motor assume efficiency,power factor and other term if neccecery
hi friends if you have any 400KV Substation Erection and installations Drgs please send to me.My email id:kandi.suresh441@gmail.com
if my load is not in continuous operation so what type of panel is required APFC or fixed capacitor bank without APFC whether C.T is required in both cases compulsory? explain detail
How can calculate the earthing strip of Copper/GI for rating of 30kV,discharge current 10KA Lightning arrester.
can you tell me/show me, how to manually synchronize 2 DG. preferred with video.
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage. note--it is tested with 5000 kv megger and insulation resistance is 0.05 M ohm. and some time 0.03 M ohm comes.
1. what is the meaning of bus? 2. what is the dc transformer? How it work 3.what is the function of the serge absorber? 4.How the CT and PT rating calculate/
on what factor insulation resistance depends
What is basic impulse insulation level? And how it is calculated for sub- station?
How to know any size of cable if there are not written on cable? Answer must be theurical not by experience.
WHAT IS THE FAULT WHEN 100HP TURBINE MOTOR TRIPS, LIST THE FAULTS AND ITS TRABULESHOOTING TIPS.. MY AUTO TARNSFORMER STARTER TRIPS
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)