What is Primary and Secondary Injection Test of CT and
Relay.
Answers were Sorted based on User's Feedback
Answer / roy
primary injuction means we will inject the current in the
primary of the current transformer. and according to the CT
ratio and relay setting the relay will operate.
secondary injuction means we will disconnect the wires from
the secondary side of the CT and inject the current to the
relay directly. the relay will operate according to its
threshold.
Is This Answer Correct ? | 23 Yes | 5 No |
Answer / yusuff ibrahim sipchem
Primary imnjection test- to test the circults including the primary circuit, i.e the CT by injecting the current to the busbar at low voltage, thew current will be according the busbar system rated current
Secondary injection test-to test the secondary circuit ony, whcih includes the relay and secondary wiring only. CTs can't be tested with this. in this the current will be normally 0-10Amps
Is This Answer Correct ? | 6 Yes | 8 No |
Why do we use 36KV LAS for 33kv line and 9KV LAS for 11KV line?
What is the power factor of a transformer at no load?
during the period of armature reaction ,if the brush shift is not accomplish, what happen?
WAT IS MEANT BY COLD AND HOT START OF A MOTOR?? HOW DOES IT AFFECT A MOTOR'S PERFORMANCE??
why phase & neutral is use in tv? why earthing not use ?
what is active network?
What is IDMT relay how it works.
3 Answers Electrotherm, Sulzer,
Can XLPE/SWB/PVC (P3) 7C X 2.5mm2 be replaced by Can XLPE/SWB/PVC (P2) 7C X 2.5mm2??? P3 vs P2
I have a CT meter with ratio 60/5. The meter reading of previous month was 3290.49 and that of current month was 3797.26. How many chargeable units as per normal meter should be my reading.
What should be the voltage between neutral and earth of a UPS?
When are the directional relays used?
please send me previose rrb junior engineer qustion papers