why neutral busbar size is half of the phase busbar size in
control panels
Answer / abdul samad
If ur Load is balanced in three Phase supply system Neural
current is Zero . neutral current is always depend on the
Unbalance load. So in Case of 3 phase system neutral bus
taken half of Main bus.
but in case of 1 phase supply system neutral is the return
cunductor and phase current will be equal to neutral curent.
so In 1 phase neural would be of same size.
as In three phase, current in neutral in one third
of phases so conductor size is less. but in single phase neutral conductor size should be same as phase conductor size
Is This Answer Correct ? | 6 Yes | 4 No |
can we use 220 volt 15 w a.c. lamp on 220 volt d.c.
What is servo motor and what are the applications of servo motor?
How to Preparation of online test
can we use ELCB and RCBO in one db
how to identify the failer of igbt
How to get a multiplier in 11kv energy meter?
Is there any problem about which the drive (inverter) doesn't show/display the alarm and/or fault but instead of this , it doesn't work ? I want to know that could there be any kind of problem in the drive when the drive doesn't display the alarm and/or fault ?
Why we are using LA Rating 10kA in 66 kv substation
For my plant the electricity department charging some amount for t/f losses. May i know what are transformer losses
In zero voltage we can pass supply to our body means we cant get shock its true ? how we can do it ?
what is the purpose of using battery in dg sets, please specify in details.
The coils having selfinductancs 10mh and15mh,effective inductance 40mh when connected in series aiding. what will be the equivalent inductance if we connect them in series opposing?