what is the function of buchhos rely in transformer
Answers were Sorted based on User's Feedback
Answer / ilononurb
Buchholz is a gas actuated relay which response if there is
any abnormality inside the transformer. Ex. If there a
incipient fault happens in transformer winding. arc causes
decomposition of oil that contains more hydrogen gas which
being light rise upward to bocholz relay. The gas is
collected to upper side of the relay. therby oil level drop
down in the B-relay that tilt the mercury switch that close
the alarm circuit.B-relay gives an alarm so that the
transformer can be disconected before the incipient fault
grows in to serious one.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / prashant
when there is any abnormal condition like
overloading,overcurrent,or any such things which increase
the tempreture of oil,,,then there will be gas bubble in
oil,,,,buchhos relay senses this abnormal condition,,,,
it will also give alarm signal if oil level is lower than
pre decide value,,,,,,,,,
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / kjh
I agree with answer #2 .I want to add some, B-relay has two
stages one is connected in alarm circuit and the other is
connected wtih tripping circuit.It also tripping the
incomming C.B. of the transformer in case sewear fault.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / atti
Actually Ans # 04 option # B IS not the function of b-Rely.The
function of B-REly is the smoke detection not to check the
leakage.Allthough It has a oil leve detector .
| Is This Answer Correct ? | 0 Yes | 0 No |
It is known as BUCHHOLZ relay.
A buchholz relay is operated by the accumulation of air bubbles within a transformer.
a) When a short circuit happens within the windings or within the contacts of the tap changer or any other shortings a localised heating takes place and gasses are liberated within the transformer.
b) When there is a leak in the transformer and the oil level drops or
c) The temp drops too low and the oil level falls below the required level.
These conditions trigger the float switch within the buchholz relay. The contacts are used for tripping the transformer or to on an alarm.
| Is This Answer Correct ? | 0 Yes | 2 No |
how much kn lightning arrestor is used in 11kv line
Is it possible to convert Dependent sources to its equivelent current or voltage Sources ?????
WHAT IS THE FUNCTION OF SHORT CIRCUIT MAINTENANCE CT
The basis on which voltage selection of motor is done i.e. either HT or LT.
how to find motor contactor rating and bimetalic relay rating? of 30kw motor which will operate on star-delta starter?
What is C check in a diesel generator and what are parts and what has to be done during the C check
What is critical disruptive voltage?
When the relative speed between the magnetic fields of stator and rotor does is zero under steady state operation?
Can we get the shock if Power system is unearth means delta type take an rated voltage as 6.6 KV?
If connected load of Asphalt plant is 375Kw. What suitable KVA DG set is required. What is calculation formula. what extra load have to consider. in what efficiency it will work.
1. The DC generaror,s induced output emf is connected with a DC motor(as load). when increasing the load of the motor by using brake drum or any way. what are the parameters will changes in both motor and generator(voltage, current, resistance, frequency, speed, torque, power, flux etc...) 2. Similarly for AC generator and AC motor 3. similarly if using DC batteries instead of DC generator, What happens?
What are dcs and plc?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)