Why Batteries are rated as AH i.e AmpereHour,and its
formula to converting AmpHour to Amp
Answers were Sorted based on User's Feedback
Answer / prashant
whenever we switch on any appliance at that instants current
is the quantity that is been actually used. Batteries are
used to supply power hence forth their ratings are mentioned
in AH ( Ampere Hour ) i.e current capacity that can be
delivered in a period of 1 hour.you can divide Amp-hr by 60
to get amperes used in a minute.both are readings for
current only
Is This Answer Correct ? | 12 Yes | 4 No |
Answer / fakhir
A battery can deliver the power for limited time period.
Battery rating in AH reflects its capability to supply X
amps in a period of one hour. Operational time of a battery
thus can be extended in proportion to amps loading i-e
lower the connected load higher the service time. Thus
expressing capacity in absolute 'amps' does not make
sense.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sunil kaushik
amp-hour is means that a battery can supply toatl ahr for 20 hrs .so by dividing the amps with hous we can get the a/hr.
i do not why this is use
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / venkatesan.j
It reflets how much current it can supply for own hour, but
if reduced current is drawn then the time period it can
supply is obtained dividing the AH by current drawn.
Is This Answer Correct ? | 0 Yes | 4 No |
How much dc volt applied in cathodic protection system?
DG B-check,C-Check,D-check is depending upon the running hrs.If the running hrs is not reached as mentioned.How to conduct the DG checks.
In star and delta connected systems , for driving power and as well as light load which one you will preferred?
what is Harmonic effect?
what is the use of static frequency converter and static excitation equipment? and where it is employed? for what?
oil sample dielectric test gives the insulation rupture voltage at 26 kv. is this transformer safe to be operated . The working voltage is 11 kv
what is vch ?
Why collecting electrode of ESP to be earthed
as we see that in our country the power rating for transmission is always rated in multiple of 11 like 11kv,33kv,66kv132kv. So i want to know wht is reason or logic here.
how circuit breaker work.. what is the operations taking place inside a circuit breaker when an overcurrent occurs... is it similar to fuse?
why indicated sypply only by 440V in 3-phase system.
HOW TO SET THE EARTH FAULT SETTINGS IN ACB????????????