i heard that power factor(PF) is the main concern for
industries, if they are maintaining PF around 0.6 they will
be fined for that. now the question is, how can they improve
the PF ranging between 0.9 to 0.95 which is safe for them
i,e escaping from the fine?
Answers were Sorted based on User's Feedback
Answer / sai
we can use the Requird rated capacitors while we can
mainten the pf
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / abdul wajid
Power factor in industries can be improved by using
capacitor banks
| Is This Answer Correct ? | 3 Yes | 0 No |
The PF is low because of inductive load. You can improve IT by adding capacitive load. Luckily cap load is loss free.That means you dont pay kwh for it but you must buy and maintain the capacitor and on and off it as necessary at the right amount.
One way to know how much you need, is you must know the load in KW and the pf.
assuming the load is 500 kw and the PF is 0.6 and you want to improve it to 0.95. you can find out the kva demands at this two pf levels
500/0.6=833kva . 500/0.95=526 kva, 833 kva -526kva =307kva
If you add 307kvar into the system in paralel you would improve the pf to 0.95 you can divide this into 8 steps of 40 KVAR each connected accros the 3 phases through an auto PF regulator.Your cap on each step will be rated as 40 kvar at 415 volts (rated voltage) 3 PHASE.
I welcome any improvements or comment about this.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / amit biswas
inddustries mostly use static variable compensation (SVC)
technique for pf improvment.
Nowwhy dose pf drops? Due to inductive loads(eg.due to
arcing furnaces)
what SVC scheme dose is it proptionatly increases
captcitacne with inc. inductance or vice versa.
also using syc. motors can improve pf
(remember sync. motor is also called sync. condensor)
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / edy
Let say the load 500kw and u wanna increase ur power factor
from 0.6 to 0.95
500 (Tan 1-Tan 2)-u can use complex calculator to convert
from cos to tan
500 (1.33-0.32)
505kvar
u can set it with 6 step
505/6
84kvar and make it 80kvar each step
| Is This Answer Correct ? | 0 Yes | 0 No |
What is cable gland,why does use for?
IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoing breaker kA rating to be equal to busbar kA rating?
What will the effect on a motor designed at 60 HZ, and operated on 50 HZ ??
Whether amorphous core transformer is commercialized or not:Name of company making amorphous core transformer and what are different rating?
Capacitor is load free component but why ampere meter shows current when capacitor bank breaker close?
What value(high/low) of diversity factor is desired in power system and why? How such value is achieved?
What will hapen if we run generator below 47.6hz frequency?
what is the difference between AHU and FCU .
Why the core in the distribution transformer is in even number
why we use capacitor in Fans not resistor?
What is CVT and what is relation with wave trap?
Why cables and busbar both needed in LT Panels?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)