how manys ways dp transmitter can be calibrated having
range of -150 to 400mmwc,what side pressure u will apply?
Answers were Sorted based on User's Feedback
Answer / basil
TWO WAYS.WE WANT TO GIVE 150 MMWC ON THE LOWER SIDE AND
ZERO PRESSURE ON HIGHER SIDE AND SHOULD GET THE OUT PUT OF
4 mA.AND ZERO PRESSURE ON THE SIDE OF LOWER AND 400 mmWC ON
THE HIGHER SIDE AND SHOULD GET THE OUT PUT OF 20mA.
IF NO PRESSURE ON BOTH SIDES THE OUTPUT SHOULD BE 8.36 mA
(IF IT IS A 4-20mA TRANSMITTER)
| Is This Answer Correct ? | 21 Yes | 2 No |
Answer / naresh makhwani
We always have to apply pressure on the high side of the
transmitter. You cannot apply pressure on the lower side,
though if you will apply it gives you the negative reading.
| Is This Answer Correct ? | 15 Yes | 4 No |
Answer / jigar anadkat
You Can Calibrate in Two different Ways:
1) By applying normal pressure according to the range i.e.
(-150) mmwc with vacuum pump and observe 4 mA and keeping
this pressure on LP side apply 400 mmwc in HP side and
observe 20 mA (in steps).
2) Apply 150 mmwc on LP side and observe 4 ma [HP-LP=0-150
= (-150 )], then keep LP side open 0 mmwc and create
550mmwc (400+150) span by applying pressure on HP side and
observe 20 mA (in steps). If no pressure on both the side
your TX will give o/p = 8.36 mA
| Is This Answer Correct ? | 2 Yes | 1 No |
What is the procedure of changing a Faulty Module of Allen Bradley PlC without stopping the Process
In close vessel/ drum why we use d.p. transmitter of -ve range i.e. (-)500 to 0 mmwc.
Sir, I want junior executive, Instrumentation question papaer for IOCL, Plz send to arabinda.ghosh83@gmail.com
what is difference between RTD , thermo couple and thermistor in general ?? (except temperature co-efficient )
What should be the ideal tapping location for pressure differential transmitter for liquid service. If the tapping taken from the top of the pipe then PDIT will work properly or not. If PDIT do not work properly then what minimum corrective action should be taken in order to solve wrong tapping locations.
what is the full formof HART
how u calibate pr tx without master tx?
Can I calibrate the Electromagnetic Flow Meter on line and How.
How to connect another 24 volt dc power supply in circuit when previous power supply has become weak.what is the connection?
2 Answers Bhole Baba Dairy Industries,
what is control valve and how is work
why we are giving negative supply for vibration sensors?
Give me a simple formula to calculate the bore of orifice plate with datas avilable instead of BS 1040.I want to calculate the approximate bore size only.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)