why ht motor connection in star
Answers were Sorted based on User's Feedback
Answer / avdhesh
HT motors operates on high voltage ( 6.6 or 11KV). IF we
make delta connections than voltage experianced by windings
will be line voltage, which will require more insulation of
winding. In star connection voltage experinced by each
winding is phase voltage hence less insulation is required.
This is the reason HT motors always wound in star
connection.
| Is This Answer Correct ? | 86 Yes | 1 No |
Answer / anand
Ht motor star connection current is root 3 times low carried & power saving but delta connection current is high
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / svrao
HT motors operates on high voltage ( 6.6 or 11KV). IF we
make delta connections than voltage experianced by windings
will be line voltage, which will require more insulation of
winding. In star connection voltage experinced by each
winding is phase voltage hence less insulation is required.
This is the reason HT motors always wound in star
connection.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / narayanaswamy
I am of the opinion that star connection of HT motor is done to have better operation of protective gear
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pankaj gajare
Because HT motor having large starting current so that if
your connection will be in star then your current will be
root three so its automatically reduce.
its star delta principle...in star connection current will
root three times reduce.
| Is This Answer Correct ? | 3 Yes | 10 No |
Answer / jameel
the ht motor connection in star because it is easy and
cheaper than delta connection in high voltage and star
delta connection not used in this system .
and the best question here why the ht capacitor of power
factor connection star not delta although the delta
connection is more economecal than star. we need in star
three times farad(reactive power) of ccapacitor than delta
but we connection star not delta because the same reason in
ht motor.
but the ht transformer some times it is necssary to
conection the primary or the secondary or both delta
accrding to the requirment of network.
| Is This Answer Correct ? | 2 Yes | 9 No |
Answer / priti
in star connected sysytms...u can provide it with a
neutral..so that in case of faults the fault current will
flow through the neural nd hence preventing shocks!!
| Is This Answer Correct ? | 1 Yes | 9 No |
While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply
How much ph is maintained of water resistance starter for slipring induction motor ?
in soft starter system for 375 KW 3 ph induction motor for multi stage vertical pump, two thyristers failed causing shorting of thyrister. the motor winding failed while starting.What is the cause and what is the effect in above case
do any one help me to get "C" license,, i have doubts ,,, if mediators ter pls call me,, my no is 8056640042
why C.T protection required for H.T.lines?
where is used dc volage transformer,and what is highest capacity of transformer
When electric field is parallel to the plane of incidence, the electromagnetic wave is said to be a.Linearly polarized b.circularly polarized c. Elliptically polarized d. Hyperbolically polarized
how to calculate optimum loading for transformer?
what happens if dc supply is given and the remedies for it.
What is the cut-off rate?
what mean by machin
how make to Incident and accident report
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)