why ht motor connection in star
Answers were Sorted based on User's Feedback
Answer / avdhesh
HT motors operates on high voltage ( 6.6 or 11KV). IF we
make delta connections than voltage experianced by windings
will be line voltage, which will require more insulation of
winding. In star connection voltage experinced by each
winding is phase voltage hence less insulation is required.
This is the reason HT motors always wound in star
connection.
| Is This Answer Correct ? | 86 Yes | 1 No |
Answer / anand
Ht motor star connection current is root 3 times low carried & power saving but delta connection current is high
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / svrao
HT motors operates on high voltage ( 6.6 or 11KV). IF we
make delta connections than voltage experianced by windings
will be line voltage, which will require more insulation of
winding. In star connection voltage experinced by each
winding is phase voltage hence less insulation is required.
This is the reason HT motors always wound in star
connection.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / narayanaswamy
I am of the opinion that star connection of HT motor is done to have better operation of protective gear
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pankaj gajare
Because HT motor having large starting current so that if
your connection will be in star then your current will be
root three so its automatically reduce.
its star delta principle...in star connection current will
root three times reduce.
| Is This Answer Correct ? | 3 Yes | 10 No |
Answer / jameel
the ht motor connection in star because it is easy and
cheaper than delta connection in high voltage and star
delta connection not used in this system .
and the best question here why the ht capacitor of power
factor connection star not delta although the delta
connection is more economecal than star. we need in star
three times farad(reactive power) of ccapacitor than delta
but we connection star not delta because the same reason in
ht motor.
but the ht transformer some times it is necssary to
conection the primary or the secondary or both delta
accrding to the requirment of network.
| Is This Answer Correct ? | 2 Yes | 9 No |
Answer / priti
in star connected sysytms...u can provide it with a
neutral..so that in case of faults the fault current will
flow through the neural nd hence preventing shocks!!
| Is This Answer Correct ? | 1 Yes | 9 No |
is there any current and voltage drop on liquid resistance starter water/soda tank ?
defination of controlled shunt reactor
Why Auto Transformer is called "Auto"? What is the logic?
how to calculate the loss tangent of electrical cables
How to convert resistance value at 20 degree to 90 degree?
What are the Safety Steps While Inspection the LT Panel.
The iron loss in a 100kva transformer is 1 kw and full load copper losses are 2 kw, then what is maximum efficiency occure at a load?
How to distinguish between the armature wires with the field wires of a Dc motor ?
why should the lowest unit of a testing transformer ( cascaded transformer ) have higher power rating??
My system is 22kv/3.3kv transformer. client is asking to use NGR, but as we have dedicated Neutral Earthing systems which has a value less than 1 Ohm. So i want solid comparision. Why i should not use NGR as my system is already protected.Can any one help me to get out of this.how should i reply on basis of some great comparision and calculations. Please help
what is lightning arester?generaly which type of used in industeries? why its used?
What is thresh hold value of current?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)