what is the relation between Sq mm of wire and its current
carrying capacity?
Answers were Sorted based on User's Feedback
Answer / jk
Standard quation R=1/a and I=1/R
a=cross sectional area in Sq.mm
R=Resistance in ohms
I=Current in Ampere
now if we shorting above two euation in one form the the
formula become I=a means current is directly proportional
to the cross-sectional area of cable.inshort if cross-
sectional area increase then the current carrying capacity
is also increase of the cable.
| Is This Answer Correct ? | 29 Yes | 7 No |
sq mm means areaof crossection of the conductor
R prportional L/A
I=1/R
I=A/L
I= CURRENT
L= LENGTH OF THE CONDUCTOR
A= AREA OF CROSSECTION OF THE CONDUCTOR
SO AREA INCREASES ,CURRENT CARRYING CAPACITY ALSO INCREASES
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / chiplonkar
Current carrying capacity of a wire depends on the thermal
properties of the insulation applied over the conductor.
i.e. its temperature withstanding capacity decides the
current carrying capacity. For sending higher currents in a
wire,one must have lower resitance in order to limit the
Heat generated in the conductor.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / s.vijayakumar
it is correct but this answer for dc current or AC current
| Is This Answer Correct ? | 4 Yes | 6 No |
After completing iti in electrician, how can i get certificate of electrical supervisor? What ia requirements. For it?
what is shunt trip coil? what was the function in rmu?
Form S and "c" license application both are same? @ tneb portal
ful form of gis
why rating of transformer is in KVA but of motor is in KW
What is an ideal transformer?
why neutral and earth should not be connected on 3 phase 440v/50c/s supply at consumer side. where as on 25kv/ac/50c/s railway traction substation neutral and earth will be connected and track at substation. and track will act as neutral and earth. Reasons for this is needed urgently
what is meant by unity power factor?unity means one why dont call 2,3,4......?
How many types of relay are present in a VCB and ACB, what are the tests we can conduct on both breakers and how to set the relays values
What is plc and how to do preventive maintenance
Why do we will ground the positive terminal in electrostatic precipitator
In hydel power plants, L.A's, S.C's are placed inside the control panel boards. what is the purpose? [already the total body was earthed to ground.]
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)