how to check IR values in alternator winding?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Isolate all phase windings at both ends and measure IR of
each phase to body and between windings
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / subash
A. Purpose and Theory
The IR test measures the resistance of the electrical
insulation between the copper conductors and the core of
the stator or the rotor. Ideally this resistance is
infinite, since after all, the purpose of the insulation is
to block current flow between the copper and the core. In
practice, the IR is not infinitely high. Usually, the lower
the insulation resistance, the more likely it is that there
is a problem with the insulation.
PI is a variation of the IR test. PI is the ratio of the IR
measured after voltage has been applied for 10 minutes
(R10) to the IR measured after one minute (R1), i.e.:
PI = R10/R1
A low PI indicates that a winding may be contaminated with
oil, dirt, insects, etc. or soaked with water. In the test,
a relatively high DC voltage is applied between the winding
copper and the stator or rotor core (usually via the
machine frame). The current flowing in the circuit is then
measured
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / nithin
Insulation resistance of alternator is checked using a megger and before measuring it the connections to the protective devices like CT,PT and also the connection to the AVR to be disconnected. Then the star connection of the winding to be disconnected ,then we can check IR value
| Is This Answer Correct ? | 0 Yes | 0 No |
Is it mandatory statutory requirement of transformer oil filtration annualy despite oil is withstanding required dieelectrical strenth and all others parameters
in 6.6 kv vaccum circuit breaker vaccum bottole vaccum capacity ????
How to calculate load requirement of a 50 flat apartment with 5 kw each unit,sizing of cable,transformer
what is -24vDC and how can generate this -24vDC
while doing high potential for 11KV 3 core cable how much leakage current will obtain?, what will be acceptance value?
why we connect the capacitor bank in star , not in delta in any system
what happens in the short circuited secondary transformer,if the resistance of the short circuit is increased gradually?
Do we really need wheels for the transformer
How to calculate incomer of a capacitor bank/feeder from its KVAR, AND how to calculate the copper busbar for rated incomer,like for 400A we calculate the 40x10 of aluminum busbar.
what happan when ac power transmitted in unity power factor
Explain the working principle of Vacuum circuit breaker and Air circuit breaker
10 Answers HP, Trinidad and Tobago Electricity Commission T TEC,
what is 33 /11kv transformer bdv
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)