Answer / shalini.b
Power factor is the cosine of angle between voltage &
current.i.e cos(phi)
or
It is the ratio of Active power to reactive power
cos(phi)=KW/KVA
| Is This Answer Correct ? | 20 Yes | 3 No |
Answer / suhas yeole
it is the ratio of active power to the apperent
power,i.e. cos(Q)=kw/kva
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / bijay
To Chetan,
Suppose u got 80 out 0f 100 in an exam.
this means u r at a pf of 0.8, the class topper got 95, so
his PF is 0.95.
Now note that KVA is ur total marks(100)
and KW is what u scored.
now its simple pf=kw/kva
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / mehdi
In the above:
cos(phi)=PF= KW/KVA formula is correct.
but KVA is apparent power not reactive power.
KVA= V*I ,
KW=V*I*cos(phi) ,
KVAR= V*I*sin(phi)
KVA=apparent power=Sqrt(KW*KW + KVAR*KVAR)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / anusree
Efficiency of utilisation of a power supply, higher the pf
better is the efficiency, pf is the ratio of active power
to reactive power
| Is This Answer Correct ? | 1 Yes | 5 No |
kindly arrange to send me RRB Bangalore previous question paper for JE/Electrical and JE/Signal I am going to write exam on 2010
sir please send me techinical questions for junior engineer posting in bangalore railway i am diploma holder
in domestic service connection,what is service main?
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
generally on the roadside v hav 11kv line which is being step down to 440v line to line....so any1 can tell me which type of transformer they r using whether it is star to delta,delta to star etc...???
( Re: WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR CAPACITOR BANK Answer # 1 The capacitor current would be kvar x 1000 / (415 x sqrt3). This would be 70a approx. The MCCB selected should have *atleast 1.4 times this current i.e. 1.4 x 70= 98. So you should choose at least 100 A mccb.) regarding to this answer,i would like to know why the current have to times 1.4 to get the right amphere for the mccb.hows the formula to get the 1.4??tq
Advantages of using bundled conductors ?
why we multiply 11 in High Electric supply?(eg.11KV, 33Kv, 330Kv etc.)
Transformer type...??
Between Turbo alternator and Hydro alternator which one is more difficult to cool and why?
What happens when the power factor is leading and its disadvantages.
Why is making current of CB always greater than CB breaking burrent?.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)