phase clearance between phase to phase and earth
Answers were Sorted based on User's Feedback
Answer / s pradhan
For 11 KV;Ph-Ph-130 mm
Ph-E -100 mm
For 6.6 KV:Ph-Ph-90 mm
Ph-E -70 mm
For 415 V :Ph-Ph-25 mm
Ph-E -20 mm
| Is This Answer Correct ? | 54 Yes | 19 No |
Answer / geetha
For 415 V :Ph-Ph-25 mm
Ph-E -20 mm
For 6.6 KV:Ph-Ph-90 mm
Ph-E -70 mm
for 11 KV : Ph-Ph-229mm
Ph-E-178 mm
for 11 KV : Ph-Ph-229mm
Ph-E- 178mm
for 33 KV : Ph-Ph-320mm
Ph-E-320mm
for 132 KV : Ph-Ph-1100mm if Lightning impulse = 550
Ph-E- 1100mm
Ph-Ph-1300mm if Lightning impulse = 650
Ph-E- 1300mm
for 220 KV : Ph-Ph-1900mm if Lightning impulse = 950
Ph-E-1900 mm
Ph-Ph-2100mm if Lightning impulse = 1050
Ph-E-2100 mm
| Is This Answer Correct ? | 28 Yes | 10 No |
Answer / saleem
phase clearance between phase to phase and earth in
11Kv,33Kv and 66kv System.
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / mathi
ans: 110mm for phase to earth
130mm for phase to phase
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / sinnadurai sripadmanaban
Please give clearances for indoor as well as for outdoor and in air/vacuum/SF6 or within a switchboard(enclosure-IP..)
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / bmw6633@gmail.com
phase to phase 1inch and for earth 1 1/2 inch
| Is This Answer Correct ? | 11 Yes | 25 No |
What are the advantages and disadvantages of oil filled transformers?
2 Answers Mercantile Marine Department, Studio College,
can we use generator(a.c) as a motor.if so how if not why.
In the N-series schneider reclosers. What is the difference between current during fault time and current at tripping? This appears in the Event log in an event of a trip out.
Why increase in current leads to increase in conductor temperature?
what is Real power and Reactive power ? what is difference between them ?
What is main difference between earthing and neutral grounding?
On what factors the generating voltage depends ? Generating voltage are (3.3kV, 6.6KV , 11KV, 13.8kV) Why so ?
what is the resultant phase shift in a 3 phase power system including neutral if on or more phases gets grounded or short circuited. kindly explain in detail for the reasons...
how test transfomer(3 phase75kva) by megger
IN 1000kva transformer where the oil and winding temperature sensors is connected
What is type of transformers?
Why we use a shunt capacitor or synchronizing Motor To Improve a Power factor pls reply me in this mail dinesh_elect_eng@yahoo.com
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)