phase clearance between phase to phase and earth
Answers were Sorted based on User's Feedback
Answer / s pradhan
For 11 KV;Ph-Ph-130 mm
Ph-E -100 mm
For 6.6 KV:Ph-Ph-90 mm
Ph-E -70 mm
For 415 V :Ph-Ph-25 mm
Ph-E -20 mm
| Is This Answer Correct ? | 54 Yes | 19 No |
Answer / geetha
For 415 V :Ph-Ph-25 mm
Ph-E -20 mm
For 6.6 KV:Ph-Ph-90 mm
Ph-E -70 mm
for 11 KV : Ph-Ph-229mm
Ph-E-178 mm
for 11 KV : Ph-Ph-229mm
Ph-E- 178mm
for 33 KV : Ph-Ph-320mm
Ph-E-320mm
for 132 KV : Ph-Ph-1100mm if Lightning impulse = 550
Ph-E- 1100mm
Ph-Ph-1300mm if Lightning impulse = 650
Ph-E- 1300mm
for 220 KV : Ph-Ph-1900mm if Lightning impulse = 950
Ph-E-1900 mm
Ph-Ph-2100mm if Lightning impulse = 1050
Ph-E-2100 mm
| Is This Answer Correct ? | 28 Yes | 10 No |
Answer / saleem
phase clearance between phase to phase and earth in
11Kv,33Kv and 66kv System.
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / mathi
ans: 110mm for phase to earth
130mm for phase to phase
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / sinnadurai sripadmanaban
Please give clearances for indoor as well as for outdoor and in air/vacuum/SF6 or within a switchboard(enclosure-IP..)
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / bmw6633@gmail.com
phase to phase 1inch and for earth 1 1/2 inch
| Is This Answer Correct ? | 11 Yes | 25 No |
Why GRR starts from 60% of motor speed why not less than 60%?
What is the exact minimum vale of voltage between an earth and netural which can damage or can do malfunction of the electronic equipments ? If this is mentioned in any book, pl.give reference.
0 Answers Bhushan Power Steel,
boiler is running in rankine cycle and deisel generator is....?
avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid after synchronisation it regulates power factor why....
what is phase and neutral.
How can we increase the capacity of exixting capacitor bank??????????????? PLS. Help
WHY IL=IPH IN STAR AND WHY IPH=IL/1.732 IN DELTA? WHAT IS REASON BEHIND IT?
what is tan delta point in a current transformer?
Name the test signals used in control system
During underground cabling in landscape area what did we cover the cable with to prevent the electric shock & protect the cable?
Which device of PlC does share load between DG sets when DG are running in perallel?
HOW WE CALCULATE CURRENT IF THERE ARE NOT PRESENT ANY AMMETER OR MULTIMMETER??????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)