Answer / thirukumar
each TR = 400 CFM
thumb rule
200 Sq.ft = 1 TR ..... 150 to 200 Sq.ft = 1TR
| Is This Answer Correct ? | 304 Yes | 72 No |
Answer / shashi
inorder to calculate tr you can use following formula:
Delta T in F X Flow in USGPM / 24
| Is This Answer Correct ? | 74 Yes | 31 No |
Answer / sreenivasa rao avupati
We have to do Heat load calculation where we can achieve at
Grand total heat ( Sum of Grand Sen Heat + Grand Lat Heat).
TR = (GTH*1.05)/12000 TR - GTH in Btu/Hr
Calculation of TR from CFM is a thumb rule and dependa upon
inside design conditions. For Comform applications ( DBT-
Inside 2DegC & 55% RH we amy consider 400 Cfm per 1 TR).
In case of low temperature ( DBT:23+/-2 Deg C and RH <50%
this can be 250 to 300 Cfm per 1 TR.
But my recommendation is to do rough Heat load calculation
which can give the appropriate TR requirement.
Regards,
| Is This Answer Correct ? | 24 Yes | 5 No |
Answer / ramakrishna m.r.
each TR = 350 to 400 cfm as per manufacture
thumb rule
150 to 170 Sq.ft = 1 TR should not cross more than 180 sq.ft
| Is This Answer Correct ? | 35 Yes | 22 No |
Answer / mahesh
Actually we are following the 1 TR =400 CFM consider it should be re-circulation system, because of we consider less T.R compare to Once-through system ,so 200 to 300 CFM for 1 T.R suitable for Once-through system.
otherwise 400 CFM consider for Once-through system AHU Capacity will be increased.so better to consider 200 to 300 CFM for Once-through AHU's.
Any answer or formula recording above concept ,please share
| Is This Answer Correct ? | 4 Yes | 1 No |
What is BKW of Motor. And what its significance
When charging a 20 MVA , 33kV/6.6kV transformer through regulated (0-6.6 kV or 0-33 kV) source on no load , what will be the maximum current drawn by transformer from source and what sould be the source capacity.
What do you mean by cogeneration? What its working principle?
difference between turns ratio and transformation ratio?
when voltage increases then current also increases then what is the need of over voltage relay and over current relay? can we measure over voltage and over current by measuring current only?
the power consumption of perminant magnet moving coil?
Why transformer neutral earthing? What is advantages?
what are effects of harmonics in the three phase a.c power system ?
working principle of generators?
In Induction machines which type of emf is induced ( statically or dynamically)?
Either the Armoured Earthing strip of HT 3 core cable have to pass through CB CT or not , why ???
if we use a normal natural thundering; than approx how much amount of electricity we generate?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)