How to calculate the CFM to TR?
What is the Formula
Answers were Sorted based on User's Feedback
Answer / thirukumar
each TR = 400 CFM
thumb rule
200 Sq.ft = 1 TR ..... 150 to 200 Sq.ft = 1TR
Is This Answer Correct ? | 289 Yes | 66 No |
Answer / shashi
inorder to calculate tr you can use following formula:
Delta T in F X Flow in USGPM / 24
Is This Answer Correct ? | 71 Yes | 29 No |
Answer / sreenivasa rao avupati
We have to do Heat load calculation where we can achieve at
Grand total heat ( Sum of Grand Sen Heat + Grand Lat Heat).
TR = (GTH*1.05)/12000 TR - GTH in Btu/Hr
Calculation of TR from CFM is a thumb rule and dependa upon
inside design conditions. For Comform applications ( DBT-
Inside 2DegC & 55% RH we amy consider 400 Cfm per 1 TR).
In case of low temperature ( DBT:23+/-2 Deg C and RH <50%
this can be 250 to 300 Cfm per 1 TR.
But my recommendation is to do rough Heat load calculation
which can give the appropriate TR requirement.
Regards,
Is This Answer Correct ? | 23 Yes | 5 No |
Answer / ramakrishna m.r.
each TR = 350 to 400 cfm as per manufacture
thumb rule
150 to 170 Sq.ft = 1 TR should not cross more than 180 sq.ft
Is This Answer Correct ? | 35 Yes | 22 No |
Answer / mahesh
Actually we are following the 1 TR =400 CFM consider it should be re-circulation system, because of we consider less T.R compare to Once-through system ,so 200 to 300 CFM for 1 T.R suitable for Once-through system.
otherwise 400 CFM consider for Once-through system AHU Capacity will be increased.so better to consider 200 to 300 CFM for Once-through AHU's.
Any answer or formula recording above concept ,please share
Is This Answer Correct ? | 4 Yes | 1 No |
Is RTCC panel needs any control supply.
what is lightning arester?generaly which type of used in industeries? why its used?
The iron loss in a 100kva transformer is 1 kw and full load copper losses are 2 kw, then what is maximum efficiency occure at a load?
what is reactive power?, why its measured in VA ? is it transient behavior of system?
In n high voltage 11kv system What happened if 1 of CT cable (IDMT) loose.Will e/f or o/c trip.please explain detail
In constant power region of 3-phase IM torque-speed characteristics, if frequency increases voltage A does not alter B decreases C increases D none of above
limitation of conductor height on ground when we consider EMC
what is the working principle of tube light?
Why P.f. of the system decreases when it is connectect across induction motor? & how to maintain the p.f. of system to unity.?
Why underground cables are used to connect transformers?In addition how are they again connected to lines after step up or step down?
how to calculate the megger values for motor, cables and transformers?
What is converter transformer? Diff b/w converter transformer and distribution transformer? why we use converter transformer in place of giving supply to drives?