How to calculate the CFM to TR?
What is the Formula
Answers were Sorted based on User's Feedback
Answer / thirukumar
each TR = 400 CFM
thumb rule
200 Sq.ft = 1 TR ..... 150 to 200 Sq.ft = 1TR
| Is This Answer Correct ? | 304 Yes | 72 No |
Answer / shashi
inorder to calculate tr you can use following formula:
Delta T in F X Flow in USGPM / 24
| Is This Answer Correct ? | 74 Yes | 31 No |
Answer / sreenivasa rao avupati
We have to do Heat load calculation where we can achieve at
Grand total heat ( Sum of Grand Sen Heat + Grand Lat Heat).
TR = (GTH*1.05)/12000 TR - GTH in Btu/Hr
Calculation of TR from CFM is a thumb rule and dependa upon
inside design conditions. For Comform applications ( DBT-
Inside 2DegC & 55% RH we amy consider 400 Cfm per 1 TR).
In case of low temperature ( DBT:23+/-2 Deg C and RH <50%
this can be 250 to 300 Cfm per 1 TR.
But my recommendation is to do rough Heat load calculation
which can give the appropriate TR requirement.
Regards,
| Is This Answer Correct ? | 24 Yes | 5 No |
Answer / ramakrishna m.r.
each TR = 350 to 400 cfm as per manufacture
thumb rule
150 to 170 Sq.ft = 1 TR should not cross more than 180 sq.ft
| Is This Answer Correct ? | 35 Yes | 22 No |
Answer / mahesh
Actually we are following the 1 TR =400 CFM consider it should be re-circulation system, because of we consider less T.R compare to Once-through system ,so 200 to 300 CFM for 1 T.R suitable for Once-through system.
otherwise 400 CFM consider for Once-through system AHU Capacity will be increased.so better to consider 200 to 300 CFM for Once-through AHU's.
Any answer or formula recording above concept ,please share
| Is This Answer Correct ? | 4 Yes | 1 No |
We have three phase dg of 12kva rating.If the load of each phase is not constant.That means one phase drowning more load than remaining two phase..Then what will happen to dg?
how to select the isolation tranformer for siemens 802dsl cnotroller
A MACHINE WHICH HAVE 1000rpm SPEED IS LARGER IN SIZE AS COMPARED TO THAT OF A MACHINE WHICH HAVE 1500rpm.WHY ?
What are the different types of circuit breakers?
What is the previous name of Cox's Bazar
what is the applicatyons of the slipring motor and please tel me more about the slipring concept
how to calculate the slowness and fastness of energy meter if we have different kw load for example (0.746 kw and meter rev constant 400 and we calculate the 2 rev in 30 sec) please explain the formula thanks
1 Answers WAPDA Water and Power Development Authority,
The capacity of the transformer is 20/25 MVA, Ratio is 132/11 KV, Vactor group YNyno. and impedance is 10.07%. As per the calculation the secondary current is 1312.2Amps. The maximum fault current the transformer should sustain is 13.030KA. How many times the transformer should sustain the maximum short circuit current of 13.030KA over a period up 1 Year. The transformer is repaired one & 10 Years old.
what is IP 55 & IP 54 ?
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
types of transformer ?
What are the different types of VVVF Drive ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)