how to calulate multiplying factor if meter ratio is /5 ampere
and ct ratio is 100/5 ampere.(our supply is 3 phase 415
volts)what is multiply factor?
Answers were Sorted based on User's Feedback
Answer / sandy
if ct ratio is 100/5A then multiplying factor will be 20.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dharminder singh
tell me the multiply factor rahul singh
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rahul singh
M.F= Line CT ration/kwh meter ratio
if kwh meter have /5 ration then you have to install 100 in
pri ration in kwh meter
Is This Answer Correct ? | 0 Yes | 1 No |
what is 30-phase of transformer
If the (Motor control center)Panel work on field the relay used in panel in the case this will be damage and no indication provide on panel.fault occur in panel and MCB will not trip. how happen the relay damage in panel and what effect of panel.
How will you calaculate the Ct ratio based on connected load 500KVA,and 11KV supply ?
what is the difference b/w winding insulation class and winding temperature class?
While connecting the flood light plug on to the 415 V distribution panel,there was spark and the cable got burnt. Three ignitors of the flood light also burnt of. The lamps are of 400 W (total 6 lamps) connected through 1.5 mm2 cable. The plug was immediately removed from the circuit. There was a 30 mA RCD connected and a 250 A MCCB; however both did not trip. What could be the possible reasons for the circuit devices not to trip?Can someone assist please. Additional info if needed can be provided.
what is sevice settings for mccb?How can be it setted?
what is the difference between skin effect
WORKING PRINCIPLE OF VACCUM CKT BREAKER ?
WHAT IS THE SETTING OF OVERLOAD RELAY AND UNDER VOLTAGE RELAY IN PERCENTAGE?
Basic philosophy of applying 3P tripping for uptill 132KV switchyards & for 132KV & above 1P/3P tripping is used.
how the earhing is done on ship and airplane.
reason of capacitor failure or low voltage in alternator wtih 10kva dgset