I need the proper answer on :-
What is the Earthing Value as per the standard for Raw
power and UPS Pit and in panel /DB N-E value ???
Answers were Sorted based on User's Feedback
Answer / k.p.sharma
The Earthing Value as per the standard for Raw
power and UPS Pit SHOULD BE LESS THAN 2 OHM and in
panel /DB N-E value SHOULD NOT BE MORE THAN 5 VOLT.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / rathod manhar
For raw power and UPS pit the earth resistance value is
around 1 ohms and N-E value is 1-0.5 ohmsfor good earthing.
Is This Answer Correct ? | 2 Yes | 0 No |