I have tow 200 KVA UPS, both are in parallel mode.My
question is that, both are running on battery when power
fail, if one of them fail (Eg rectifire fails or some other
reason), at thet time reverse power will come to faild ups
if it comes then it will harm to failed ups or not? if not
then how it protects to faied ups????????????????
Answer / sathishkumar
hi you mean both the UPS in PRS(parallel redundancy systen)
mode.then u have to connect the battery back to each UPS
separately.untill unless we are using as single sourse we
should not connect the both possitive terminals of Battery
bank connection in a common bus bar.if any one UPS failed
and EB power also goes off the entire load will be shifted
to single UPS which is working good condition also the
Battery bank which belongs to that battery bank only
support to the load.
remember in PRS mode output only paraled not input sources
(AC mains and battery back up)
| Is This Answer Correct ? | 2 Yes | 0 No |
If an electrical component has a positive temperature coefficient, how come such components have high power losses due to heat if current decreases when resistance increases? assuming power given by I^2*R whereby the Resistance is infinite.
what is the unit of current
Which are the major Nuclear power accidents in the world?
when neutral will carry the current?what could be the magnitude?
Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0
why the earth pin is thicker than other pins in a plug? If it is for reducing resistance, then why the copper earth wire is not so thick as earth pin of socket?
Formulae for calculating the transmission line losses for different voltage levels
why the value of k is more in shell typr transformers?
what is slip resistance? how much its value in 110 kw motor? why voltage is varied in vvvf drive ?
i work as a technician at a private company.. i used to take amp reading for certain appliances such as air con.. the problem is when i clamp the neutral, wire there is a current reading.. from my understanding for single phase system neutral should not have current unless if the circuit is not complete.. yet the air con still work
How do you select a cable size(Cu&Al) for a particular load
10 Answers Adhunik, BPCL Bharat Petroleum, Hiecon, TATA,
What are safety features considered for Lifts during emergency?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)