What is ics,icu,icw of load breaker
Answers were Sorted based on User's Feedback
Answer / mike evans
Circuit breakers are designed with withstand short circuit
currents for a short period of time, defined as Icw for a
period of 1 second. This is designed to guarantee
selectivity of breakers and other devices providing short
circuit current protection. The ultimate breaking capacity
of the breaker is the highest symmetrical short circuit
fault current that the breaker is designed to break, and the
breaker manufacture is required to guarantee this level of
performance for one time only. Ics or service breaking
capacity must be guaranteed at least 3 times.
Realistically, the value of Icu is not practical when
considering fault calculations in a distribution system, and
often manufacturers aim for achieving Ics=Icu.
Is This Answer Correct ? | 147 Yes | 26 No |
Answer / ravikumar varatharaj
Icu - ultimate short-circuit breaking capacity
a breaking capacity for which the prescribed conditions according to a specified test sequence do not include the capability of the circuit-breaker to carry its rated current continuously
Ics - service short-circuit breaking capacity
a breaking capacity for which the prescribed conditions according to a specified test sequence include the capability of the circuit-breaker to carry its rated current continuously
Icw - rated short-time withstand current
The rated short-time withstand current of a circuit-breaker is the value of short-time withstand
current assigned
Icm - short-circuit breaking (or making) capacity
a breaking (or making) capacity for which the prescribed conditions include a short circuit
Is This Answer Correct ? | 40 Yes | 9 No |
Answer / tad rybak
To my understanding Icm stands for Short Circuit Making
Capacity.
According to standard IEC 947-2 or BS EN60947, etc.
It is equal to 2.2 x Icu, where Icu means Ultimate breaking
capacity.
Is This Answer Correct ? | 53 Yes | 31 No |
Answer / vyara
Ultimate or rated short-circuit breaking capacity
(Icn - EN 60898)
A breaking capacity for which the prescribed conditions,
according to a specified test sequence do
not include the capability of the MCB (Miniature Circuit
Breakers) to carry 0.96 times its rated current for the
conventional time.
Ultimate short-circuit breaking capacity
(Icu - EN 60947-2)
A breaking capacity for which the prescribed conditions,
according to a specified test sequence do
not include the capability of the MCB to carry its
rated current for the conventional time.
Service short-circuit breaking capacity
(Ics - EN 60898)
A breaking capacity for which the prescribed
conditions according to a specified test sequence
include the capability of the MCB to carry 0.96
times its rated current for the conventional time.
Service short-circuit breaking capacity
(Ics - EN 60947-2)
A breaking capacity for which the prescribed
conditions according to a specified test sequence
include the capability of the MCB to carry its rated
current for the conventional time.
Is This Answer Correct ? | 19 Yes | 20 No |
how to select a air/vacuum circuit breaker.is there any thumb rule???
How to select the gauge of wire for winding of motors? How to select number of turns for winding of three phase induction motor?
in three 3.5 core aluminium ug cable. one cable is used for one phase by shrting R,Y and B wires and other 2 cables used for Y and b phases. balace 3 neutral wires are made common and connected to load. suddenly neutral current was more than line current what is the reason behind this?
What are n circles?
What is an alternator impedance value?
why capacitors cant used in genset to maintain power factor..??
explanation of mesh bus bars
What is the basic difference between synchronous machine and induction machiine?