Tell the details of the precommissioning tests that are
performed on distribution transformer, power cable and
switchgear (11kv).
Answer / subaharan
first check the transformer bushings and their condition,then
you meggering the transformer each phase to phase and phase to
earth.
power cable you check the high voltage test which is used for
measuring the leakage current,meggering and continuity
checking.
switchgear the same meggering,isolator checking,relay
testing(set various values of currents,voltages and set time
for tripping) make the fault and note the trip time.
| Is This Answer Correct ? | 1 Yes | 0 No |
why the generator will take 8 to 12 hours to start after it got interrupted due to technical problems in case of power plants.
How much DC or AC Current that a Human Body withstand for Electrical Shocks?
what is the diff.between neutral and earth?
what is th basic difference between a d latch time line and a d flip flop time line???
What is VCB? Where it is installed?
What is auto changeover and how it works plz write details.
how can we save enegry by using VFD for Resiprocating Air compressor which is having more unloading running hours
its Kva and Kv are same?
When neutral is grounded in electrical circuit?
what is max. continous current of LT side of distribtion transformers? ie for25kVA, 63kVA, 100kVA, 200kVA etc
WHAT IS THE DIFFERENCE B/W THREE POINT STARTER AND FOUR POINT STARTER
what type of transformer used in soft ware parks its distribution or power transformer. like 1800 kva
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)