Generally in AC we consider voltage, frequency and phase
sequence for parallel operation ... Can we parallel two DC
battery chargers? If yes, then what precaution to be taken
when we parallel two DC power?
Answers were Sorted based on User's Feedback
Answer / vijaykumar shetye
1) Yes, theoretically, we can parallel two DC battery
chargers, but generally they are not designed for parallel
operation.
2) Following factors are to be considered.
1) The voltage of both the chargers should be the same.
2) Both chargers should be connected in the same
polarity.
3) The output impedance of both the chargers should be
the same, so that both deliver equal current. (It is not
necessary that both the chargers should be of the same
make. It would rather prefer same model than same make.)
4) The characteristics of both the chargers should be the
same. Both should be set at the same current setting for
changeover from boost to float.
5) The current capacity of both the chargers should be
the same.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / pankaj verma
Main criteria for parallel connection is :
1. Both chargers should be connected in the same polarity.
2. Voltage of both the chargers should be same.
3. chargers should have identical specification.
Practically chargers are never used in parallel, they are
just momentarily paralleled in order to shift load of each
other so that maintenance work on each one can be carried out.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / omkar
) The voltage of both the chargers should be the same.
2) Both chargers should be connected in the same
polarity.
3) The output impedance of both the chargers should be
the same, so that both deliver equal current. (It is not
necessary that both the chargers should be of the same
make. It would rather prefer same model than same make.)
4) The characteristics of both the chargers should be the
same. Both should be set at the same current setting for
changeover from boost to float.
5) The current capacity of both the chargers should be
the same.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod
DC battery charger is feeding the float& DC load curent,
when AC fails battery will feed the DC,if charger fails
another charger can put in service.DC battery chargers not
required to parallel.(ie. battery having C10 capacity 100
AH or more)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ramprasad
Before parallel operation of two DC Battery charger
precaution to be taken is
1. Both Battery charger must to be same make.
2. Output of Battery charger output must to same volt.
3. Primary of both charger must to be connected in parallel
with same phase sequence.
4. Output of Charger connected in parallel with same
polarity.
5. Voltage regulation must be very perfect of charger.
| Is This Answer Correct ? | 5 Yes | 8 No |
In cable sizing calculation (determining the max route length of cable) why we choose the shortest length between cable length of full load current Iflc & starting current Istart?
state the disadvantages of carbon filament???
374kvar capacitor bank connected across 600kw,6.6kv motor.what will happen if motor run at 50% , whether full kvar applied or half?
What is the bundle conductor?
what is the means of dedicate earthing?
In scott connected transformer number of turns in the primary winding of teaser transformer is % of number of primary turns of main transformer A 86.6 B 57.7 C 14.4 D 33.3
how to combine two linear transformers...............
What are the types of TESTS in CIRCUIT BREAKERS based on Testing and commissioning?
why on delay timer used for fully automatic star delta starter?
Whether we used insulated line for 33KV supply. what we called it.
we have two generators different capacity on 15 MW and other 6MW at 11 KV , 15 MW gen. bus short level current 40KA,and 6MW short level current 25KA,, length of cable 100MTR between 6 MW from 15MW gen. for bus coupling . kindly tell any one can we use both NGR OR one NGR from any GEN. BOTH NGR has diff. rating. Tariq pakistan
why we testing the core balance of the transformer before comissioning?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)