Generally in AC we consider voltage, frequency and phase
sequence for parallel operation ... Can we parallel two DC
battery chargers? If yes, then what precaution to be taken
when we parallel two DC power?
Answers were Sorted based on User's Feedback
Answer / vijaykumar shetye
1) Yes, theoretically, we can parallel two DC battery
chargers, but generally they are not designed for parallel
operation.
2) Following factors are to be considered.
1) The voltage of both the chargers should be the same.
2) Both chargers should be connected in the same
polarity.
3) The output impedance of both the chargers should be
the same, so that both deliver equal current. (It is not
necessary that both the chargers should be of the same
make. It would rather prefer same model than same make.)
4) The characteristics of both the chargers should be the
same. Both should be set at the same current setting for
changeover from boost to float.
5) The current capacity of both the chargers should be
the same.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / pankaj verma
Main criteria for parallel connection is :
1. Both chargers should be connected in the same polarity.
2. Voltage of both the chargers should be same.
3. chargers should have identical specification.
Practically chargers are never used in parallel, they are
just momentarily paralleled in order to shift load of each
other so that maintenance work on each one can be carried out.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / omkar
) The voltage of both the chargers should be the same.
2) Both chargers should be connected in the same
polarity.
3) The output impedance of both the chargers should be
the same, so that both deliver equal current. (It is not
necessary that both the chargers should be of the same
make. It would rather prefer same model than same make.)
4) The characteristics of both the chargers should be the
same. Both should be set at the same current setting for
changeover from boost to float.
5) The current capacity of both the chargers should be
the same.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod
DC battery charger is feeding the float& DC load curent,
when AC fails battery will feed the DC,if charger fails
another charger can put in service.DC battery chargers not
required to parallel.(ie. battery having C10 capacity 100
AH or more)
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ramprasad
Before parallel operation of two DC Battery charger
precaution to be taken is
1. Both Battery charger must to be same make.
2. Output of Battery charger output must to same volt.
3. Primary of both charger must to be connected in parallel
with same phase sequence.
4. Output of Charger connected in parallel with same
polarity.
5. Voltage regulation must be very perfect of charger.
Is This Answer Correct ? | 5 Yes | 8 No |
why we use 630mm single core cable for transformer secondary side and why two neutral cable
How to Calculate KA Rating of Main LT Panel
what is torque & how it will produce & what is the formula for that.
What is mean A32 B32 C32 D32 in mcb(miniature circuit breaker)
Whether it is possible to measure energy at the input of rectifier transformer (12 pulse with very high odd harmonics)
in breather of transformer how sillicon gel absorb the moisture?wat happen when the moisture in that oil?
In a Synchronous generator, Can AC voltage be used instead of DC voltage in field winding of rotor to produce AC power?
In auto transformer if power transferred inductively and conductively are same, the ratio of output/input voltage is A 1 B 0.7 C 0.5 D none of above
The synchronous machine excitation system explain
Define the three phase formula fuse.
ELECTRICAL DRIVES: can a motor load system with passive load torque can have equilibrium speed in second quadrant
In a Dyn11 transformer, how are the 3 windings of the delta connected? Assume that R1-R2, Y1-Y2, B1-B2 are the 3 windings on the HV side.