WHAT HAPPEN IF GENERATOR TURBINE IF TRIP?
Answers were Sorted based on User's Feedback
Answer / santosh chinchalkar
If T.G set is running on synchronus speed and turbine is
triped on low steam pressure or some other resion, The
Generator will take the power from system instated of
giving and Generator will work as Motor,that will harmful
to Turbine blades.for avoiding this reverse power
protection are used to stop the Generator.
Is This Answer Correct ? | 49 Yes | 4 No |
Answer / ashiesh
The gemneraTor wiLL start behaving as motor, & will consume
power instead of generating.
But will simply stop if it has a reverse power protection
system.
Is This Answer Correct ? | 14 Yes | 1 No |
Answer / ramji
The Generator will run still since there some steam trapped
in Turbine.This suitation is called Low Forward Power since
there is not enough Steam to run the Generator in desired
speed.This occurs because of some trapped steam in turbine
for some seconds.Now Days special vents doors are designed
in turbine to release these steam on account of tripping of
turbines
But Normally in protection Trip Logic of Generators there
will be Class:A,Class:B,Class:C
For Class A Gen Breaker will trip for below faults
U/V Stage-2 , O/V , Low Forward Power,Reverse Reactive
power,Neg Ph Seq ,Over Voltage
For Class B Turbine Breaker will Trip which also trip Gen
breaker instantly for below faults
Differential protection , Restricted Earth Fault .....
For Class C Grid Breaker will trip for below faults
Over Frequency and Under Frequency Under Voltage stage-1
and Over voltage
Because when you trip Gen Breaker for Undervoltage it will
result in whole plant black out so for stage-1 tripping of
grid breaker will do
similarly for All turbine faults the Gen Breaker is tripped
so that it is isolated from the system
Is This Answer Correct ? | 17 Yes | 4 No |
Answer / vivek
main breaker will be trip and annunciator will show
tripping prob.
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / dayal varma
automatically the output of the generator stop.
Is This Answer Correct ? | 16 Yes | 9 No |
Answer / vikas kallewar
TURBINE RUNNING IN SOLO MODE. if turbine trip at that time
generator also trip. due to under frequency,under
voltage,and 86T WILL TRIP TO 86G.
TURBINE RUNNING IN PARRALAL MODE GENERATOR TRIP TO RPR
PROTECTION
Is This Answer Correct ? | 5 Yes | 2 No |
When Turbine trips, the dc excitation voltage which is
applied to the rotor through slip ring also trips,so no
excitation was there in the rotor means no flux cutting in
the stator.So generating voltage will be zero. So it will
nither act as generator nor as a motor. Its simply rotate &
due to moment of inertia,it will come to zero in short time.
Is This Answer Correct ? | 10 Yes | 14 No |
WHAT IS IM (INDEX OF MOUNTING )IN MOTORS
why do we have another cartridge filled with oil fitted at the bottom silica gel cartridge in power transforers
what is the meaning of Dd0yn11
While HT line put on to activate ACB in low tention panel VCB tripping instantly.why it happens
what happen if generator exitation lost?
what is the difference between AHU and FCU .
as per standards how many neutral earthings and body earthings are needed.please help me
why transformers rating are in KVA
what is 3rd Harmonics? how it is generated in alternator
what is deffrent alternatid and gernater
how tan-delta test is performed?
wath is this mining of dg