what is excitation system explain in detail with its
working?
Answer / mike
1) A.C. excitation.
This type of the exciter operated with a.c. supply and rated frequency around 50 until 250 Hz.The output provide with slip ring to be rectified for internal mounted diode cubicles.This types can replaced for commutator on the d.c with solid state rectifier.
The output from rectifier supply to the generator rotor with slip ring for the d.c excitation system. Usually a pilot exciter made from a permanent magnet for supply to main exciter.
For the main exciter,it commonly made in three phase used the combination of diode in a bridge formation.The bridge arm have a several piece of diodes in parallel condition.
The method for short circuit protection is each diode individually fused to remove it from the electrical circuit in when it happen.
2) Brushless excitation.
This excitation system have a similar function between A.C excitation with advance application.The rectifier diode installed on the exciter shaft.The main exciter has its output armature winding on the rotor with its field on the stator.
Normally for rotor output frequency rated around 100 and 250 Hz and it is connected to the shaft mounted diodes.The rotor of main generator can supply the output with directly application.
The pilot exciter can be a permanent magnet generator with frequency operation until 400 Hz.For the small generator,supply can provide from generator terminal to the exciter field.
3) Thyristor excitation.
For this type of excitation system it used thyristor rectifier to directly control the generator filed current and it can response with faster system by controlling the exciter field current.Thyristor excitation fed system is necessary to provide slip rings and brushes to connect to the machine rotor.
This function is important to alert and response to the error or faulty for system stability due to critical application.But it have disadvantage because this system not been developed commercially and not common system for generator at around the world.It also difficult to providing the reliably control signals to them from stationary equipment.
Excitation power may be provided with direct application to the coupled main and pilot exciters or it can fed from main generator terminals using a step down transformer.
Normally the transformer ratio is design to provide full output during the occurrence of a system fault and it reduces the machine terminal voltage for protection system.
Is This Answer Correct ? | 2 Yes | 0 No |
shall we use a machine having 60Hz frequency in india ? why?
Role of active and reactive Power sharing in between two synchronized Generators, Droop Setting role ?
what is relation between torque and speed / rpm?
what happen if generator exitation lost?
at the time of starting back emf of a motor is zero.so how can it will start to run??
Control wiring of a dol starter for forward and backward
There is any especial requirement for motor to drive through with VFD?
in house wiring when two wires are same colour coding and there is no any connection one end how to find which wire is earthing wire
In india, according to trade theory above 5 HP motor reqired star delta starter. But we R connect 11 KV motor with 14MW in Direct to line ( With VCB starter combination) Can U Guess, How it is possible ?????
what is the function of RMU?
what is diffrenance between ACB and Isolator
what happen if any one phase of a slipring induction rotor winding is open?is it start or won't?