what is excitation system explain in detail with its
working?
Answer / mike
1) A.C. excitation.
This type of the exciter operated with a.c. supply and rated frequency around 50 until 250 Hz.The output provide with slip ring to be rectified for internal mounted diode cubicles.This types can replaced for commutator on the d.c with solid state rectifier.
The output from rectifier supply to the generator rotor with slip ring for the d.c excitation system. Usually a pilot exciter made from a permanent magnet for supply to main exciter.
For the main exciter,it commonly made in three phase used the combination of diode in a bridge formation.The bridge arm have a several piece of diodes in parallel condition.
The method for short circuit protection is each diode individually fused to remove it from the electrical circuit in when it happen.
2) Brushless excitation.
This excitation system have a similar function between A.C excitation with advance application.The rectifier diode installed on the exciter shaft.The main exciter has its output armature winding on the rotor with its field on the stator.
Normally for rotor output frequency rated around 100 and 250 Hz and it is connected to the shaft mounted diodes.The rotor of main generator can supply the output with directly application.
The pilot exciter can be a permanent magnet generator with frequency operation until 400 Hz.For the small generator,supply can provide from generator terminal to the exciter field.
3) Thyristor excitation.
For this type of excitation system it used thyristor rectifier to directly control the generator filed current and it can response with faster system by controlling the exciter field current.Thyristor excitation fed system is necessary to provide slip rings and brushes to connect to the machine rotor.
This function is important to alert and response to the error or faulty for system stability due to critical application.But it have disadvantage because this system not been developed commercially and not common system for generator at around the world.It also difficult to providing the reliably control signals to them from stationary equipment.
Excitation power may be provided with direct application to the coupled main and pilot exciters or it can fed from main generator terminals using a step down transformer.
Normally the transformer ratio is design to provide full output during the occurrence of a system fault and it reduces the machine terminal voltage for protection system.
| Is This Answer Correct ? | 2 Yes | 0 No |
why do we use 3 single phase instead of one 3 phase?? though vee connection is its advantage but what is the hidden reason behind it??
i have DEEE certificate in vinyaka misson unive rsity. is a INGNO if possible get the electrical C licences in Tamil nadu?
why are distributed windings generally used in alternators?
What is dielectric loss?
What is the function of the exiter in DG.
what is meant by class 1 E in electrical power supply?
1- XC and the RC time constant are both measures of the reaction of C to a change in ____? 2-The power factor is a numerical ratio with a value between 0 and 1 equal to the ______________ of the phase angle. 3-When V and I are out of phase because of reactance, the product of V times I is called ______________ power 4-For _____________ inductors, the branch currents can be added algebraically. 5- The ______________ power in watts can be calculated as I^2R 6-Calculate XL with L = 30mH and f = 1kHz ( I have Xl=2piFL 2*3.141592653*1kHz*30mH =188 ohms Please check) 7-A parallel RL circuit has the values, R = 5kohms, XL = 5kohms. A voltage source of Vt = 10Vrms is connected in parallel to R and L. Determine the total current, It delivered by the voltage source Vt. 8-A series RC circuit has R = 1Mohm and C = 1microF. How long would it take for the capacitor to fully discharge if it is initially fully charged? 9-A circuit has real power = 300W and an apparent power of 500VA. Determine the power factor and phase angle. 10-The time constant for an LR series circuit is T = 0.1s and R = 10ohms. Calculate the inductance L.
why magnetising curve not start with zero voltage?
do we need NGR panel when the output of the genset is LV but after that it is step up to 22 kv. condition is 12 genset 400v are operating in parallel.
Double Busbar Scheme for outdoor switch yard system (132kv) step up power plant Hi friends 1. in this system both busbars energized all the time. 2. what is the meaning of main BB and transfer BB, 3. step up transformer connect main bus bar all the time or both BB connected through DS switch . 4.bus sectionalization means ? thank you.
why 30 ma elcb is used ?why cant 100 ma?
Z transform is use when system is not a) converges b) diverges
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)