how percentage impedence effect on the size of the power
transformer?
Answers were Sorted based on User's Feedback
Answer / jaswinder
% impedence is use to determine the max fault current the
transformer is capable of delivering to a downstream short
circuit.
Fault current=FLC*100/%imp.
this fault current is use to cal fault MVA
Fault MVA = 1.732 x fault current x V.
eg: If transformer of 2000kVA,5%imp having flc of around
1200A is use to supply to a motor of same flc carrying
capacity and if the voltage drop at transformer terminal is
more than the permissible voltage drop (+- 10%)during
stating of motor then the above transformer will be of
lower rating hence we have to select the transformer rating
higher than 2000kVA eg:-3000kVA (In other words transformer
having higher SC current capability ).If voltage remain
within the rated voltage of the motor then no oversizing of
tranformer is required.
| Is This Answer Correct ? | 8 Yes | 1 No |
A 4-Pole D.C. Generator has a speed of 1500r.p.m. Then what will be the frequency of D.C. Generator ?
What is the mmf,rgt and ngt please brief completely
can anyone tell me can the electromagnetic waves can be reflected back?if so how &by which material it can be reflected back?please tell me so that it can help to my wireless power trasnmission device.
how choose conductor&depending upon load
on 22.03.2015 at 17:15hrs Y phase 66kV class Power Trf-2 Current transformer has flashed over and oil came out. The failed CT has been replaced on 24.03.2015 at 13:15hrs and the Trf has been charged in presence of RT Hassan after conducting the pre-commissioning tests. On the same day at 17:00hrs the commissioned CT has again flashed over and immediately the Trf has been isolated from power supply. It is confirmed the secondary is not opened and checked the earth integrity and is found ok. Here what would be the reason for the CT failure?
Why we are testing cables with dc?
On which side, taps are provided in tap changing transformers and why?
How to Calculate Transformer Earthing Electrode Rod Size both Body and neutral Earthing ? Any Standard Formula? Please Suggted
1)we have 1000 cfm Blower,Dia-1Mtr,Velocity of air 94 m/s 2)We have Natural Air velocity 94m/s 3If i Put Wind Mill in natural air ,speed is 94m/s Then it will generate Assume 100kw 4)If i put same wind mill across the Blower,air speed is same 94m/s now the Question is Will it generate 100 kw?
what r the safety measures in UPS ? explain all?
how to test an MCB
how to test a motor from megger
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)