how we can check that any motor is faulty may be single
phase or three phase?
Answers were Sorted based on User's Feedback
Answer / p.senthil kumar
1.you can check the ohmic value by using multi meter in
between r-y,y-b,r-b of motor windings & it must be the same
ohmic value for fine motor winding.
2.also check insullation value of each winding R,Y,B with
reference to earth.in that megger meter must shown infinite
value for fine motor winding condition.if it is shown zero
motor stator winding is defective.
3.for single phase check for connectivity of winding in
between running & starting winding.also check for a faulty
capacitor.
Is This Answer Correct ? | 13 Yes | 0 No |
Answer / monika hassan
sigle phase or three phase the test protocols are same as
per IS325. By conducting priliminary test like IR value
measurement, resistance measurement, No-load run test etc.
all these tests ensures the healthy ness of the machine.
Is This Answer Correct ? | 12 Yes | 0 No |
Approach of a cooling tower is the difference between temperatures of what factors?
What is shunt voltage and u v voltage witch one best
Why battery is always operate on dc supply?
1 Answers Vikram Ispat Industries,
i HP = ?? 746 watts or 735.5 and how??
for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?
why generaters need four earthings
WHAT IS THE TOTAL POWER GENERATION IN CHHATTISGARH?
why use -48 volt DC power in telecom?
What will happen when we will connect lamp in between phase and earth.
Multimeter show phase to neutral volt 230 the per phase but phase to phase 415 not show 460 why.
ACCORDING TO IEC WHAT SHOULD BE THE MINIMUM HEIGHT OF G.I. STRUCTURE OF CT, PT, ISOLATOR, LA?
if flow of electrons is current then why their direction are different???