What is ELR, and where it is used ?
Answers were Sorted based on User's Feedback
Answer / giri
ELR is earth leakage relay,as its name indicates it's used
for protection against earth leakage.
| Is This Answer Correct ? | 89 Yes | 5 No |
Answer / rk
ELR or commonly known to be EL CB . all 3phsaes and netral
of the incommin supply passs throuh oone ring type ct so
that there will be no current in CT secondary if there is
healthy system but in case there is a ground fault at load
end the cT will record the unbalance current and the relay
will sence the fault.beacuse durring ground fault the fault
curent will pas througth ground to the sourcr insted of
throug the neural inside the ring CT.
| Is This Answer Correct ? | 40 Yes | 3 No |
Answer / roshan thakur
ELR is earth leakage relay.this is very sensible for leakage.and this is generally used in panel for protection if MCCB.
| Is This Answer Correct ? | 21 Yes | 3 No |
Answer / tushar
Just I want to know about ELR. We have connected ELR With Incoming panel(800A). That ELR is getting Trip within Seconds. Equipments are not getting any Earth Leakages. No shock effect from equipments… I am not able to Understand what is exact problem..Pls Let me know Reason.
| Is This Answer Correct ? | 1 Yes | 0 No |
this full name is earth leakage relay . basically relay
used in diffrential current transformer
| Is This Answer Correct ? | 14 Yes | 26 No |
what is black out?,what is brown out?
why we need to us lenz's law for synchornous motor
TYPES OF TEMPERING OF ENERGY METER
What is the difference between Earth Fault protection & Neutral Protection
practicalLY what is impedence ...?
why it is mentioned as 8/10 mva transformer why not directly 8mva or 10mva transformer. please explain me the full detailed reason.
how can we know the size of cable cross-section from current rating ?
what is XLPE type cable
if ELCB and RCCB connected in series,what wiil be the result
how to select the automotive wire size by mathematical calculation. for xenon headlamp with ballast. the ballast given data voltage 10-17v,current permenant 6amp, run up phase is 15amp, peak at swicth on max 400micro sec is 40amp.the sum of cable resistance is 150mohm.please provide referenc document if any for relating the peak at switch on current,time & wire wire size
how many types of colling system it transformers?
What is Phase to Phase clearance for 800V System Operating Voltage as per IEC61439
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)