I HAVE CONSUMER WHOSE POWER FACTOR IS 65% I WANT TO INCREASE
IT TO 98%.HOW TO CARRY OUT?
Answers were Sorted based on User's Feedback
Answer / mubashar ali
you can calculate VRAr, those required for improvment 0.65
to 0.98
KW(Tan1-Tan2)
KW= your total load
Tan1= cos invers of first pf ,than take tan1
Tan2= cos invers of second pf, than take tan2
then u find total KVAr reqird , and installed same rating
capictor
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / mrt
by adding capacitors parallel to the load we can increase
the power factor.Now a days APFC will regualtes the power
factor
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / hm
Power factor improving devices:
1. capacitor banks
2. synchronous condensers
3. phase advancers etc.
synchronous condensers are used in industries but for low
power customers capacitor banks are useful. but only
disadvantage is that if supply voltage does not remain
constant, reactive power generation by capacitor varies so
power factor cant remain at 98%, it fluctuates.
so don't install rated capacitor banks directly,add a
voltage regulator circuit to maintain constant voltage or
better to use APFC.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / navin
reqd KVAR = KW ( Tan (cos-1 P1) - Tan ( cos-1 P2) )
KW- Load KW
P1- Existing PF angle
P2- Desired PF angle
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / zahid noor
Now a days Automatic Power Factor Control Panels can be
easily purchased from Panel manufacturer by providing them
the details of load, voltage level, current etc & existing
PF , can contact m/s Universal cables Satna, M/s L&T
Switchgear, and some local manufacturers can also supply as
per requirement.
| Is This Answer Correct ? | 4 Yes | 4 No |
PROVIDE YOUR LOAD IS VERY USEFUL FOR FINDING OUT
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / rahul
to increase the power factor from 65% to 98%, the consumer
may install certain equipments such as INDUCTION MOTOR etc
which works at leading power factor and hence draws the
lagging reactive component and hence increases the overall
power factor!!!!!!!
| Is This Answer Correct ? | 2 Yes | 10 No |
simple way to find busbar sizes??
In CT's they mentioned 400/5 or 1250/5, 1000/1 here 400,1250,1000 is Breaker Capacity what is the /5 Explain me briefly
Latching current is slightly less than ?
why sometime we get electrical shock while touching the ballon of dish tv connection ? which we should not get.
what is the formula to find battery back up of ups?
what is the principle of motor
what happen if generator of micro hydro running at only a small percentage of its capacity, as a comparison, if the diesel generator that runs on only a fraction of its capacity there will be a wet stacking
What is the estimated total hydropower potential of india?
i have 1500 kva generator how much maximum load avilable of use
I would like to install the largest KW alternator to a 200 amp aluminum bus box in my home. Is it possible to install a 250 KW 400v 251amp synchronous alternator to my home?
what are the shades for mimic diagram i.e for 3.3kv,6.6kv,11kv,22kv and 33kv? which is the IS for mimic diagram?
WHAT ARE THE CHARACTERISTICS OF AN VOLTAG AMPLIFIER
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)