why do we use bundle conductors instead of using single
conductor of larger size for high voltage transmission?
Answers were Sorted based on User's Feedback
Answer / sandeep samant
It is due to skin effect of ac current. The most of ac current flows through the outer(circumference) part of conductor. So we use bundle conductor to increase the circumference area of conductor. it increases the current carrying capacity of conductor.
| Is This Answer Correct ? | 27 Yes | 10 No |
Answer / vikalp dhiman
Extreme High Voltage carrying lines causes corona loss.to reduce this loss we use bundled conductors.These consists of 2,3,or many more conductors in bundle.Each conductor carries equally distributed among these conductors(in bundle).Due to this corona loss reduces
CORONA LOSS--High voltages ionises nearby air which causes power loss and affects communication wires.
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / ali
Bundle Conductors are preferred instead of single conductor because:
-reduces voltage gradient
-affect critical corona voltage
-reduce inductive reactance
-reduce Radio Intereference
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / amit kumar beniwal
In AC transmission line if conductor Diameter increase then
Skin effect increase due to high concentration of current
near outer surface of the conductor & due to this cause
Corona loss also increase.SO we use bundle conductors
instead of single conductor.
BUNDLE CONDUCTOR -When we combine number of conductors as a
conductor whose Diameter is small is called Bundle conductor.
CORONA LOSS-Hissing noise & luminous glow due to high
voltage ionises nearby air which cause power loss and also
effect communication signals.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / rakesh kumar
we know that resistance is inversely proportional to the area of conductor, in bundle conductor two or more conductor make a bundle which increases the area of the conductor. this means we reduces the resistance of the conductor and the power loss is reduces.it also helpful to reduces the skin effect and corona loss..............
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / ritesh a. wajari
because of more is the diameter less is the corona loss,
genaraly in bundle there is four conductor so it maintain the more distance so it reduced the corona loss.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / saleem pasha
Voltage gradient is reduced because of less diameter of conductor hence bundeled conductor is used instead of single conductor for high voltage transmission line
| Is This Answer Correct ? | 0 Yes | 0 No |
-How do you select cable size for a given load at a given distance from source of supply. How do you find voltage drop.
how did the differential relay work to protect the power transformer
Can I parallel 1 MVA generator with 1kVA Generator? if V, F, Ph Seq and Ph angles are same
RELAY 1. REF RELAY : • OPERATION WITH CT CURRENT FLOW DIRECTION. • WHY REF RELAY WHEN DIFFERENTIAL RELAY IS THERE. • REF RELAY STABILITY CHECK BY PRIMARY INJECTION – WHICH POINT FOR CUR RENT INJECTION. • WHY REF RELAY NEED STABILISING RESISTOR. IF RESISTOR SHORTED OR BYPASSED, WHAT WILL HAPPEN. • WHICH TYPE OF RELAY FOR REF, HIGH IMPEDANCE OR LOW IMPEDANCE. • IF NEUTRAL CT IS NOT CONNECTED IN THE CIRCUIT, WHAT WILL HAPPEN. • REF PROTECTION ACTS ON WHICH OF FOLLOWING: SINGLE PH. TO E/F; PH-PH TO E/F; THREE PH. TO E/F. 2. DISTANCE RELAY : • BASIC PRINCIPLE AND TYPES • SWITCHED MODE PROTECTION – WHY IS IT CALLED SO. • SCHEMES USED • WHY ZONE-1 SET AT 80% • SETTING RANGE FOR ZONE-2 AND ZONE-3 • HOW SINGLE PHASE TO GROUND FAULT MEASUREMENT IS DONE. • 3. WHAT IS POLARITY. CT LOCATION IF INTERCHANGED WHAT WILL HAPPEN. 4. SOLKOR RELAY: 1. WHY SOLKOR IS USED. 2. CIRCUIT DIAGRAM OF SOLKOR RELAY 3. DIFFERENT PARTS OF RELAY 4. HOW IT WORKS. 5. EXPLAIN BY VECTOR DIGRAM. 6. WHAT ADVANTAGE FOR USING SUMMATION TR. 7. DIFFERENCE BETWEEN R & RF WITH CIRCUIT. 8. ADJUSTMENT OF PADDING RESISTANCE. 9. WHAT IS LEAKAGE CURRENT AND HOW TO MEASURE. 10. WHAT HAPPEN IF LINK IS LEFT OPEN. 11. 5KV/15KV INSULATION TR. ARE USED IN WHICH SYSTEM. 12. WHAT PRECAUTION TAKEN DURING TESTING. Relay Page 1 of 5 13. PROCEDURE BEFORE TESTING AND AFTER NORMALISATION. 14. HOW RELAY IS TESTED IN LIVE CONDITION. 15. RANGE OF SPILL CURRENT ANS SETTING OF RELAY 16. IF MEASURED CURRENT IS 5MILLI AMPS, CAN RELAY OPERATE. 17. EACH FAULT APPROXIMATE VALUE OF PICK UP. 18. WHAT IS THE REASON SOLKOR-R MODE PILOT SHORTED CONDITION RELAY CURRENT PRESENT. 19. AFTER SHUTDOWN, WHY NEED TO OPEN SOLKOR PILOT, IF NOT WHAT WILL HAPPEN. 20. AFTER NORMALISING WHAT CURRENT TO BE MEASURED, WHAT IS ACCEPTABLE LIMIT. 21. WHAT HAPPENS IF PILOT OPENS FROM RELAY, WHEN FEEDER IS LOADED. 22. CAN WE USE THIS RELAY AS O/C OR E/F RELAY. 23. ANY RELAY OTHER THAN PILOT CABLE TYPE. 24. IF FEEDER TRIPS ON SOLKOR, WHAT TO DO. 25. WHAT HAPPENS IF PILOT POLARITY REVERSE. 26. WHAT HAPPENS WHEN CT SHORTED AT ONE END. 27. WHAT HAPPENS IF PILOT SHORTED – STATUS OF RELAY 28. WHAT HAPPENS TO RELAY ,IF POWER CABLE GETS OPEN. 29. WHAT HAPPEN IF PADDING RESISTOR IS SHORTED AT ONE END. 5. TR. DIFFERENTIAL: 1. CIRCUIT DIAGRAM 2. DIRECTION OF FAULT CURRENT. 3. WHEN THE FAULT IS IN ZONE AND OUT OF ZONE. 4. CT CONNECTION IN PY. AND SY. SIDE. 5. BIAS SETTING AND BIAS CURRENT. 6. WHICH BIAS SETTING USED IN TRS. FOR HIGHER TAPS. 7. PURPOSE OF RESTRAINING BIAS COIL. 8. WHY BIASING REQUIRED. 9. EXPLAIN IPCT, FOR EXAMPLE, DYN10 VECTOR GROUP. WHY MATCHING TR. USED. 10. WHY NEED 2ND HARMONIC BLOCKING DURING INRUSH. 11. WHICH HARMONIC IS MORE 2ND OR 3RD. 12. HOW TO AVOID FALSE TRIPPING IN DIFF. PROTECTION WHEN INRUSH CURRENT FLOW DURING TR. IS ENERGISED. Relay Page2 of5 6. DIRECTIONAL RELAY: 1. CIRCUIT FOR USE OF DIRECTIONAL PROTECTION SYSTEM. 2. WORKING ZONE / NON-WORKING ZONE. 3. HOW THE CORRECT DIRECTION OF FLOW OF CURRENT IS DETERMINED. 4. CT & PT CONNECTION DIAGRAM. 5. SETTING OF PHASE & EARTH FAULT ANGLE AND OPERATING REGION. 6. WHICH DIRECTION IT IS PROTECTING. 7. WHAT PROTECTION AVAILABLE FOR POWER TR. 8. WHY CT CONNECTION IS STAR, IF TR. WINDING IS DELTA. 9. DIFFERENCE BETWEEN REF AND DIFF. RELAY 10. WHERE IS O/C & E/F RELAY CONNECTED EITHER HV SIDE OR LV SIDE AND HOW E/F RELAY WORKS IF TR. WINDING IS DELTA CONNECTED. 11. IN DELTA WINDING OF TR., IF ONE WINDING IS CUT AND NOT EARTHED, WHICH PROTECTION WILL ACT. 12. IF DIFF. & REF RELAY ARE NOT WORKING, WHAT IS BACK UP PROTECTION IN TR. 13. WHAT IS PURPOSE OF NGR AND HOW STANDBY E/F RELAY WORKING, TESTING PRECAUTIONS IF COMMON NGR IS USED. 14. WHAT IS PROTECTIVE ZONE OF STANDBY E/F RELAY. 15. WHAT ARE PROTECTION AVAILABLE FOR FEEDER. 16. AFTER TR. IS NORMALISED, WHAT CURRENT TO BE MEASURED. 17. BUSBAR PROTECTION: a. BASIC PRINCIPLE AND DIAGRAM WITH CURRENT DIRECTION. b. WHY OVER LAPPING CT’S REQUIRED, IF NOT WHAT WILL BE THE EFFECT. c. WHY CT SUPERVISION REQUIRED, HOW TRIPPING IS AVOIDED, WHAT IS CT SUPERVISION SETTING VALUE. d. HIGH IMPEDANCE & LOW IMPEDANCE TYPE e. TEST PROCEDURE(STEP BY STEP) f. AFTER NORMALISING, SPILL CURRENT VALUE AND LIMIT. Relay Page3of5 18. CIRCUIT BREAKER FAILURE – FUNCTION, WHY NEEDED, HOW TRIPPING ARRANGEMENT. 19. WHY INSTANTANEOUS ELEMENT IS NOT USED IN THE NETWORK. 20. WHEN FEEDER IS LIVE AND BY MISTAKE LINE EARTH SWITCH IS CLOSED, WHICH RELAY OPERATES – O/C OR E/F. 21. DURING TR. SWITCHING ON, IF DIFF. RELAY IS BLOCKED BY 2ND HARMONICS, WHAT ARE THE OTHER PROTECTION IN SERVICE. 22. WHICH OF FOLLOWING PROTECTION OPERATES FAST, WHEN 11KV CABLE COMPARTMENT GET FLASH OVER: CABLE DIFFERENTIAL; OVERCURRENT & EARTH FAULT; ARC PROTECTION. 23. WHICH PROTECTION OPERATES WHEN ANY ONE OF THE OHL PHASE IS CUT AND HANGING, NOT TOUCHED WITH EARTH. 24. WHAT ARE DIFFERENT TTB ALARMS – HOW YOU KNOW THERE IS ANY ALARM. 25. WHAT IS CIRCULATING CURRENT AND HOW IT WILL COME. 26. IF ONE TR. TRIPPED ON DIFF. RELAY WHAT YOU WILL DO. 27. IF SUB-STATION TRIP ON BUSBAR PROTECTION, HOW YOU WILL RESTORE. 28. WHAT IS CT SATURATION. HOW IT IS CARRIED OUT. 29. D.C EARTH FAULT – HOW YOU WILL FIND OUT. Relay Page 4 of5 30. PILOT WIRE SUPERVISION – HOW IT WORKS 31. IN 11KV SWITCHGEAR DBB SCHEME, ONE E/F RELAY IS FAULTY IN ONE FEEDER AND THERE IS NO SPARE FEEDER – HOW YOU WILL NORMALISE THE FEEDER. 32. WHICH PROTECTION IS USED FOR LONG CABLE FEEDER 33. DIFFERENCE BETWEEN TRAFO. DIFF. AND CABLE DIFF. PROTECTION. 34. WHAT TYPE CHARACTERISTIC AVAILABLE FOR O/C AND E/F RELAY. 35. WHAT IS THE DIFFERENCE BETWEEN STATIC AND ELECTRO- MECHANICAL O/C RELAYS. 36. WHAT IS DEAD ZONE 37. HOW TRIPPING OF OTHER ZONE AVOIDED WHEN BUS SECTION CB IN OPEN CONDITION FOR DEAD ZONE FAULT. 38. IF OUT OF STEP ALARM COMES WHILE ALL TR. IN SAME TAP POSITION, WHAT YOU WILL DO. 39. WHAT YOU WILL DO IF AN 11KV FEEDER FAILED TO TRIP ON: O/C or E/F or SOLKOR. HOW YOU RESTORE THE SUPPLY. Relay Page 5 of5
what is the transformer
Type of cable insulation?
what is transformer
Advantage of LT panel vs HT panel
What does VVVF stands for in VVVF drive ? How does it differ from VVF drive?
How do I calculate/select Droop CT ratio for various capacity of generators?
Explain cmrr?
explain why the armature voltage changes when the field rheostat is varied in self excited DC generator
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)