How to calculated capacitor rating both HT
Answer Posted / stanley electrician
capacitance of the capacitor is mentioned in KVAR.
Formula : KVAR = KW*tan@
FOR tan@, First note the power factor & KW without
connecting capacitor.
The noted power factor is in cos@.Convert the cos@ value in
tan@.
for ex. If power factor is 0.6, KW = 200
cos@ = 0.6
cos-1 (0.6) = 53.1
tan (53.1) = 1.333
200*1.333 = 266.6 KVAR
if you use 266 KVAR capacitor, Then the power factor
improves to unity (1.000).
| Is This Answer Correct ? | 20 Yes | 12 No |
Post New Answer View All Answers
Why temperature rise is conducted in bus bars and isolators?
What is Antipumping Function & If we have C.T how we find the Ratio ?
Where is the best place to mount distribution panel in a house.
In india, according to trade theory above 5 HP motor reqired star delta starter. But we R connect 11 KV motor with 14MW in Direct to line ( With VCB starter combination) Can U Guess, How it is possible ?????
Show Details FROM:Muhammed Ikram TO:qa@allinterview.com Message flagged Saturday, June 4, 2011 10:07 PMMessage bodyHello all, i want to ask a question to all of you that what is VMM (voltage monitoring module )? how it work,s? i heard somewhere that it compare 1 phase voltage to other phase voltage. but there is also some setting on it. how to set it,s setting. please tell me briefly. Thank,s and Regard,s. Muhammed Ikram.
What is diversity factor in electric installations?
WHY IL=IPH IN STAR AND WHY IPH=IL/1.732 IN DELTA? WHAT IS REASON BEHIND IT?
what is the acceptable limit value for Desolve Gas Analysis/
what happen when power factor of 2 parallely operated transformer become equle?
At what factor resistance r of a conductor depends?
What is the fault or needs to be done when frequency in ac drives is not changing?
State uses of different types of stsrters with different capacities of motors as below: a. up to 5HP b. above 5hp to 10hp c. above 10hp to 20hp d. above 20hp
What is the power factor of an alternator at no load?
what is the AC Plant and how can do the work with parts and picture tell us 150 Tr
What is MS-EXCELL?