What differance between Circuit brekar and Isolater?
Answers were Sorted based on User's Feedback
Answer / habib
Circuit breaker is device whcih disconnect the equipment
during fault condition automatically,but isolator does not
disconect the equipment automatically during fault
condition.
Isolator should be operate after deenergizing the
line,because isolator is not having any special arc
quenching facility like sf6 or vaccum in it.cb is having
this facility.
Note:- Isolator is a OFf load device it should follow the
CB operation
Is This Answer Correct ? | 66 Yes | 1 No |
Answer / aruna devi
circuit breaker is used to trip during fault condition of
the circuit whereas isolator are the off load is used for
isolate the circuit during maintenance and shutdown
Is This Answer Correct ? | 38 Yes | 1 No |
Answer / zahid noor
The basic difference between cicuit breaker & Isolator is,
Circuit breaker ,automatically breaks the circuit
electrically in conditions of fault & overload, where as
Isolator is to be switched OFF manually after tripping the
prevoius protection / drive for the purpose of
maintenance/shutdown.
Is This Answer Correct ? | 15 Yes | 0 No |
Answer / sachin
A circuit breaker is designed to break a circuit which is
carrying current at the time. Where large currents and/or
voltages are present, the opening of the circuit may induce
dangerous arcing, so means such as air blast must be used
to "blow out" the arc.
An isolator is only designed to isolate a circuit or other
component after the current has already ceased, so it
doesn't need to have any means to stop the arc.
Thus in high voltage/high current installations such as in
power stations or grid switching stations, the initial
operation to isolate the circuit, whether planned or as a
result of a fault, is by the circuit breaker, the isolator
is then used to isolate the circuit breaker for maintenance
or repair.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / ram niveth
there is no arc quenching medium in isolator .
also we have earth swith in isolator for disharge amd
safety purpose
Is This Answer Correct ? | 11 Yes | 3 No |
Answer / bedabyas
The main difference between circuit breaker and isolater is
circuit breaker can operate in any condition ie in full
load to no load condition but isolater can operate in no
load condition.
circuit breaker can operate both manually and
automatically but isolater can operate only manually.
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / shyamalmandirwala
Circuit Breaker is operated ON-LOAD whereas ISOLATOR can
not be operated ON LOAD as it does not have the arc
quenching medium as in the CIRCUIT BREAKER.
ISOLATOR is basically used for disconnecting a portion of
the power system for maintenance work to ensure safety of
persons doing maintenance work.
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / princejit singh
CB:-It is used to make or break the ciruit on no as well as
full load.
Isolator:-It is used to make or break the circuit on no load.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / pratheesh
Circuit breaker is a device which is used to cut-off a
online load in normal as well as in Faulty condition.
Which means circuit breakers are designed to cut-off a
cicuit in normal current carrying condition and also in
fault current condition. Such as to switch off a motor in
normal condition and to trip the same in fault condition
with the help of protective relays and devices.
But an isolator is a device which is designed to operate in
offline condition only. Means when there is no current flow
through it. It cannot be operated in when the circuit
breaker is closed condition. There will be both mechanical
as well as electrical interlocks for this. If u operate the
isolator when the loads connected to it running, a flash-
over will be result.
Is This Answer Correct ? | 2 Yes | 0 No |
how to select the cable size? any formula to calculate cable size?
which is better ac or dc?
What it the purpose of parallel phasing transfomers??
How vaccum is formed to create a vaccum interrupter or anything related with vaccum?
what is earthing
Can i use the B-curve MCB instead of C-curve MCB
what is stray capacitance?
Testing procedure of DG alternator stability test
What is the high series capacitance winding on high voltage power transformer ?
when ID fan will immediately stop through VFD what exactly cause and problem the ID fan
will a transformer work when pulsating dc id applied to its primary?? what will be the result??
Do any one know exacatly when the results for NHPC held on 8th march 09 for engineering trainees will be released ?. if so please post it, i'm eager to know it.