i work as a technician at a private company.. i used to take
amp reading for certain appliances such as air con.. the
problem is when i clamp the neutral, wire there is a current
reading.. from my understanding for single phase system
neutral should not have current unless if the circuit is not
complete.. yet the air con still work
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
You may not expect current in neutral of a 3phase
appliance. But there will be current in neutral of a 1
phase appliance while working.,
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / pillay
your understanding is wrong or if not
incomplete.
In any single phase circuit the neutral
is the return path
for the circuit. That means the current that
flows into the phase comes out through the neutral
Even in 3 PH balanced load you will see the
same individual ph current in the neutral but
you will see no current in the main neutral,
cos at the neutral bar the individual neutral
current had balanced up through the other phases.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / snk
yes your thinking good and by law should not be flow when
open circuit.but air con working and neutral floe is the
return of current.you make your question in tow parts then it
will be help full.
| Is This Answer Correct ? | 0 Yes | 1 No |
What are the neccessary safety arrangements before commissioning of HV substation?
how to determine kilowatts (real power) is used in energy meter? is it apparent power effect the disk rotation?
why generator is star connected ?
Rules and standards of electrical control wiring ?
When a 25kV line touches the train, will passenger get shock?
Why the suply frequency in INDIA is 50HZ
The maximum demand of consumer is 2 kW and his daily energy consumption is 20 units. Its Load Factor is (1) 10.15% (2) 41.6 % (3) 50 % (4) 60%
Why neutral cable carry current.
What is q factor?
A genarator is connected through a 20MVA ,13.8/138 KV stepdown transformer to a transmission line. at the reciving end of the line a load is supplied through a step down transformer of 10MVA,138/69 KV rating .A 0.72 PU load evaluated on load side transformer ratings as base values ,is supplied from the above system for system base values of 10 MVA and 69 KV in load circuit the value of the load in generator circuit will be ...........
WHY NOT CONSIDER PROTONS IN ELECTRICITY LIKE ELECTRIC CURRENT?
in case of induction motor when overload condition or any short ckt. why stator winding burn not to be rotor winding
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)