What is the megger value for ht
Answers were Sorted based on User's Feedback
Answer / a.manickassamy
For LT Line (In Maintenance 0.5MOhm alloweablw, Is the best
(0.410+1)X2=2.82Mohm).
For HT Line Is the best <=1Gohm.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / sateesh
it's depond upon the length of the cable & insulation of
cable.minimum value for HT< 800to 1000 ohms
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / rajesh
My question to A.Manickassamy how come this value for please describe
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mano
it's depond upon the length of the cable & insulation of
cable.minimum value for HT< 500 ohms
Is This Answer Correct ? | 10 Yes | 17 No |
How Humming noise generated in starter motor which was used the start the engine in a vehicle/car/Truck?.Moreover Starter motor was operated in DC power supply. Can you guys clarify ?
What is difference between unity power factor wattmeter and upper power factor wattmeter? In short circuit test of transformer the wattmeter used is unity power factor type or upper power factor type wattmeter?
0 Answers Jindal Steel and Power,
why the earth terminal of the three pin plug we are using bigger than the others?
How many gap between finger contact in a.c.b. and v.cb.?
1 ph induction motor winding priniple and connection diagram?Similarly for 3 ph induction motor?Full description
In synchronous generators field is rotor and armature is stator.Can we take the output at the rotor in case of synchronous generator by the dc excitation on the stator?
name the famous power plants in ap and vwhere it is located with capacity details
Is it possible to interlock between ACB & MCCB?
what size steel armoured cable is required to support 1500kva capacity. would 70mm squared be enough or would I need 90 or 120mm squared 3c plus earth
Where we use 30mA , 100mA & 300mA RCCB ?
How to do bus bar short circuit calculation for 230KV/11kv, 60 MVA Substation?
I am getting diesel genset 62 kv for my house In addition there are 6 meters of 11kv for the house Lift also being installed for house plot sise 200sq yds total 4 + 2 foloors I want to know how much earthing required how deep it should be