How to calculate kva? what is the formula.
Answers were Sorted based on User's Feedback
Answer / kumar.m
In single Phase- p=VxI/1000
In three phase - P=route3xVxIxcosphi/1000
Is This Answer Correct ? | 89 Yes | 26 No |
Answer / nick a.
square root of 3 (1.732) x E x I /1000 =kVA (3 ph )
E x I / 1000 = kVA
120 x 60 =720 /1000 = kva (single phase)
Is This Answer Correct ? | 31 Yes | 6 No |
Answer / prithvi narayan sinha
kw/kva=cos(phi)
therefore kVA=kW/cos(phi)
Is This Answer Correct ? | 21 Yes | 5 No |
Answer / aayush
For Single Phase-
P (KVA)= V (Volts) * I (Amps)/1000
For Three Phase-
P (KVA)= 1.732 * V (Volts) * I (Amps) * CosQ/
1000
Is This Answer Correct ? | 20 Yes | 7 No |
Answer / joban
p=VxI/1000 in singl phase
p=root3xVxIxCosphi/1000
Is This Answer Correct ? | 18 Yes | 7 No |
Answer / nani
some pepole are writing for power actually asking for how
to calculate KVA.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / arun reddy
Take 3phase Current for Example.
R-24, Y-29, B-27.
24+29+27=80amps
80X230 (output volt)
18400/1000=18.4KVA.
Is This Answer Correct ? | 33 Yes | 29 No |
what is diff kav & kvarh?
what is cathodic protection in Tank,and product pipelines?
DEAR SIR/MADAM,CLEARLY EXPLAIN ABOUT CRAWLING AND COGGING EFFECTS IN INDUCTION MOTOR.
My self munna.I had completed diploma from mechanical can I join facility and maintanance companys
What is difference between Electrical & Electronic Device?
7 Answers AZ Engineering, Vodafone,
what are the standard values for resistances(Megger testing) between L&N, L&E and N&E (L=Live,N=Neutral, E=Earth)?
Is it possible to measure correct value of earth resistance & cable insulation ristance with out disconncting earth lead & both sides of cable ends? If not, any other method to measure ER & CIR with out disconneting from the system.
What is the exact formula for one weber of magnetic flux?
what is the function of open delta System?
sigal phase supply is 230 v ac two phase supply is 415 v ac why three phase supply is 415 v ac why not 690 v ac
why to use 50hz only in tansmisson and as well as in distribution why not60hz?
How can calculate the earthing strip of Copper/GI for rating of 30kV,discharge current 10KA Lightning arrester.