How to calculate kva? what is the formula.
Answer Posted / arun reddy
Take 3phase Current for Example.
R-24, Y-29, B-27.
24+29+27=80amps
80X230 (output volt)
18400/1000=18.4KVA.
| Is This Answer Correct ? | 33 Yes | 29 No |
Post New Answer View All Answers
What is the difference between vector surge relay (78) and Pole slip relay (98G)
What are the different circuits in thermal power plant?
What Maximam Gap Taibaar & Bush
How cmd is calculated in case of energy neters
Draw the DOL starter and star delta starter drawing?
Describe Non I.S. Earth System and why is it used?
how to calculate vfd o/p voltage by frequency
what is the value of combined earthing in general electrical circiut?
Why the earth to phase voltage is high 250 compare to other two phases
what is size of 3phase 4wire cable to be used for 11 ton ductable A.C and how to calculate cable size for different load
WE ARE PLACE A NEW 75 KW MOTOR FOR JPF.IT IS CONNECTED IN M.C.C. WHEN WE ARE STARTING M.C.C.INCOMER IS TRIPPED.THEN WE ARE CONNECTED IN P.C.C WITH A MM30 RELAY PROTECTION THEN WE ARE STARTED MOTOR WILL RUN SMOOTHLY.
How to know about the rating(voltage and other) of induction motor if its name plate is missing at the manufacturing site.
Why we use duplex coil and hook switch in telephone system?
In ups static switch if i gives the supply at output end it will open the circuit in stactic switch or not if it will open then how it operates.
for a 400kv t/m line with 10 ampere current will corona occur?