Answer / serwox
Reasons are as follows:
Efficiency of one 3 phase transformer is slightly higher
than the overall efficiency of three single phase transformers.
Space and weight is greater for the 3 single phase tx than 1
single 3 phase tx hence cheaper to transport a 3 phase tx.
| Is This Answer Correct ? | 16 Yes | 2 No |
Answer / manthesh
we can surely use three 1-phase transformer but it cost more
than the single 3-phase transformer and maintenance cost is
high for three 1-phase transformers
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / s.p.arya
For the same rating we mostly using single 3-phase x-mer instead of the three 1-phase x-mer becoz 1. low floor space required for their installation 2.light weighted 3.cost is 15% less 4.maintenance & handling is suitable compair than three 1-phase x-mers
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / michael
We use 3 single phase transformer connected in DELTA instead of 1 single phase transformer because of:
1. space consumption
2. higher cost
3. for example 1 transformer in 3 single phase connected in delta fails to operate, still there is 2 transformer running open delta and still there is a supply in other line, rather than if 1 single phase transformer fails.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / pragati
As compared to a bank of single phase transformers,the main
advantages of a 3 phase transformer is that it occupies less
floor space, less weight,cost is less for about 15% and the
only unit is to be handled and connected.we can save iron.
saving in iron is due to the joint use of magnetic paths
between the coils.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / debashis das
Any where(motor,dianamo etc) using 3phase instead of 1
phase icrease the efficiency of convertion and also cost
saving.
| Is This Answer Correct ? | 5 Yes | 5 No |
Answer / ramkumar
one Three phase transformer will occupy less space compare
to 1 phase transformer and also maintenence is much high.
| Is This Answer Correct ? | 0 Yes | 2 No |
The rating of Transformer are 11KV, 22KV, 33KV instead of 10KV, 20KV & 30KV?
What shall be minimum thickness of firewall in between two transformers and which code specifies it ?
What is the power factor of a transformer at no load?
We have one Energy meter for Measuring the voltage,current,power,energy(KWH,KVARH,KVAH) & power factor.The problem is that the meter does not show whether the PF is lagging or leading.So i want to know that is there any way or calculation to find out that whether the PF sign (lagging or leading) depending upon the above mentioned parameters?
What is the winding resistsnce need to be in a 1000kva, 11kv/415v transformer, between ht winding to lt winding, ht winding to earth, lt winding to earth.?
What iz main protection of mediuum voltage motors and what iz the standard IR voltage of 6.6 and 11kv motors.
what is meant by 3rd hormonics ?
why are use star delta startor.
WHAT IS DIFFERENCE BETWEEN CAPACITOR AND CAPACITANCE?
Why two phase welding machine is used instead of three phase welding machine.
What is Toroid?. What is the difference between toroid and Current Transformer
what will be d.g. capacity to cater together for 14hp A.C. load & 3kw lighting load
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)