Why we are mostly using a single 3-phase transformer
instead of three 1-phase transformers?
Answers were Sorted based on User's Feedback
Answer / serwox
Reasons are as follows:
Efficiency of one 3 phase transformer is slightly higher
than the overall efficiency of three single phase transformers.
Space and weight is greater for the 3 single phase tx than 1
single 3 phase tx hence cheaper to transport a 3 phase tx.
| Is This Answer Correct ? | 16 Yes | 2 No |
Answer / manthesh
we can surely use three 1-phase transformer but it cost more
than the single 3-phase transformer and maintenance cost is
high for three 1-phase transformers
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / s.p.arya
For the same rating we mostly using single 3-phase x-mer instead of the three 1-phase x-mer becoz 1. low floor space required for their installation 2.light weighted 3.cost is 15% less 4.maintenance & handling is suitable compair than three 1-phase x-mers
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / michael
We use 3 single phase transformer connected in DELTA instead of 1 single phase transformer because of:
1. space consumption
2. higher cost
3. for example 1 transformer in 3 single phase connected in delta fails to operate, still there is 2 transformer running open delta and still there is a supply in other line, rather than if 1 single phase transformer fails.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / pragati
As compared to a bank of single phase transformers,the main
advantages of a 3 phase transformer is that it occupies less
floor space, less weight,cost is less for about 15% and the
only unit is to be handled and connected.we can save iron.
saving in iron is due to the joint use of magnetic paths
between the coils.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / debashis das
Any where(motor,dianamo etc) using 3phase instead of 1
phase icrease the efficiency of convertion and also cost
saving.
| Is This Answer Correct ? | 5 Yes | 5 No |
Answer / ramkumar
one Three phase transformer will occupy less space compare
to 1 phase transformer and also maintenence is much high.
| Is This Answer Correct ? | 0 Yes | 2 No |
can you give me some names of projects which can be used in our daily life & which is having medium cost?
WHY THE RATINGS OF TRASNFORMER IS IN KVA?
how the ac voltage are selected like 220v,415v,750v,1000v& 1.KV,6.6KV,11KV,33KV,66KV,132KV,220KV & why these are selected like these orders
what is the difference between a race around condition and toggling?
How to calculate the Sizes of the cable required for one specific load? Is there any formula for that? ( EX: For 400KW load,50mtr Length, What is the LT cable Size required?)
WHAT IS THE FAULT WHEN 100HP TURBINE MOTOR TRIPS, LIST THE FAULTS AND ITS TRABULESHOOTING TIPS.. MY AUTO TARNSFORMER STARTER TRIPS
If the t/f capacity is 500KvA then what is Amps ratting of the main breaker.
HOW MANY POLES ARE THERE IN 3 SLOTS PER POLE PER PHASE MOTOR
What is the difference between the impedance percent and impedance voltage ?
where induction generator is used ?
Define unilateral circuit?
Why wind turbines wheels rotate constantly
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)