We have one Energy meter for Measuring the
voltage,current,power,energy(KWH,KVARH,KVAH) & power
factor.The problem is that the meter does not show whether
the PF is lagging or leading.So i want to know that is
there any way or calculation to find out that whether the
PF sign (lagging or leading) depending upon the above
mentioned parameters?
Answers were Sorted based on User's Feedback
Answer / john
Is this a revenue meter from the utility company or a power
quality meter? In the case of a power quality meter, there
should be something letting you know if your PF is in a lead
or lagging. I have an Amprobe DMII Pro and it showes an i
after the PF to indicate lagging, .98i, and a c to indicate
leading, .98c. I have also seen meters with lagging PF -0.98
and leading +0.98. Another simple thing you can do is look
at your VAR, if it is in the negative, your in a lead.
As far as a revenue meter from the utility company is
concerned, call the utility company and ask them.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ram
please check the meter must be indicating sign as +
(leading) or - (Lagging) power factor.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / ds01151
By using the formula KW/KVA you can find the pf
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / ashwini
by using formula p=vicos(pf) v can calculate power factor......
| Is This Answer Correct ? | 1 Yes | 9 No |
what is high tension ? specify the range?
1 “earthing” for bonding of equipment and circuits to common plant earth electrode potential, 2 “protective earthing (PE)” when this bonding is required for personal safety provisions 3 “grounding” for interference suppressing bonding of screens, sys-tems with ground level 4. low-impedance earthing ? 5.primary earthing system and secondary earthing system what is that? 6.earthing electrode or mesh net earthing electrode ? very confusing , simple but very informative help required ? i will be very very thankful to you guys.
in wind mill use 2100 kw asychronous generator ( induction generator ) rotor voltage : 3300,stator voltage : 690, rpm : 1511 type : MRL063E04 ' we check rotor resistance magger value found following. R-EARTH - 00 M.OHM,Y-EARTH-34 M.OHM,B-EARTH- 33M.OHM R-Y: 31 M.OHM, Y-B: 00 M.OHM,B-R :33 M.OHM HOW CAN I TAKE DECISION?pls ans. quickly
What is force on a conductor in a magnetic field ?
It is used or not HT cable single core 630 sqmm in LT 3 phase capacitor bank which is used in PCC(power control center).
which is batter in construction job,ELCB or RCCB?
we have a 2.5hp Starite electric motor water pump,the elec motor burned out,we need to replace starting capacitor(old capacitor specs erased),what microfarad rating capacitor do we need? 110-125V
single phase 230v three phase voltage 415volt why we aren't used line voltage 690v?
what is the difference between multimeter and megger?
why dimmerstate always connected in star connection? what will happen if it connected in delta?
How the size of transformer decreases if we increases the frequency?
Testing report of Earthing of 3.15 MVa PTR.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)