How can w select the cable size for different rating load
& also waht r factors affecting the during selection of
cable?
Answers were Sorted based on User's Feedback
Answer / amit3456
There r so many factors for selection of cable:
1. full load of equipment or load.
2. Length of cable.
3. Derating factor.
4. Insulation level
| Is This Answer Correct ? | 34 Yes | 8 No |
cable size primarily depends on its voltage rating or kW
rating of load. From the kW rating, we can calculate the
current that should be carried by cable and the number of
runs required. we also have to calculate voltage drop
during starting and running in case of a motor load.
| Is This Answer Correct ? | 37 Yes | 18 No |
Answer / ranjan
For sizing of any feeder following are required:-
1. The load for which we are sizing
2.Dearating factor
3.pf
4.Starting voltage drop
5.running voltage drop
6.Spacing/Touching factor
7Effeciency
| Is This Answer Correct ? | 14 Yes | 3 No |
Answer / d.k.kakade
If cable size calulate on load in Amps.basis then please
give the formula, or advice cable size in 3.3kv 104Amps and
52 Amps,67 Amps, 33 Amps, and 15 Amps load.
Powe engrs.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / eng.yousef
cable size depends on:
1)total connected load via cable.
2)lenght between the source and the load.
3)temprture
4)isulator type
5)load type
6)wiring place& type
| Is This Answer Correct ? | 16 Yes | 13 No |
Answer / ch.venkateswra rao
first we consider the type of load,voltage
rating,location,power etc will be known after that we
calculate the in put current and 20% extra value will be
added to that currnet and based on that current we refer
the cable manufacture booket and select the suitable size
of the cable
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / rathinam
My point of view, To find the cable size need to divide the
LOAD CURRENT by 3.
i.e:
Cable size= Load current (10A)/ 3
= 3.3
Now the answer is 3.3, But we don't have the 3.3 size of
cable. so we can choose next related size of cable, which
is 4 sq.mm.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manishhctm
A) Firstly we have to check for wht type of system we require the cable i.e LV, MV, HV AND EHV
B) then we have to calculate first: the rated current required by load on 3phase or 1phase system i.e
1) For 3-Phase System
KVA= KW/SQRT3*PF
2) For 1-Phase System
KVA=KW/PF
C) In companies there is feeder schedule for every type of cable w.r.t the amp.
Enjoy!
| Is This Answer Correct ? | 3 Yes | 5 No |
What are the different types of testing in ht cables?
132/66kv sub-station procation ?
Please explain open transition and closed transistion system in Star delta Starter?and also the state difference of both?
The rotor current is directly proportional to slip. How?
What are the causes of having an rmu explode after installation? And how do u treat the bushings of an rmu?
Meggering minimum acceptable Ohms for insulation resistance.
Why we use startor to the motor?
Approach of a cooling tower is the difference between temperatures of what factors?
Explain what are inter-poles and why they are required in a dc machine.
why tube light flicks??
What is a dc motor?
What is the difference between the watt hour meter and Var hour meter in terms of internal connection and work theory . ie "When the meter records watt-hour an when the meter records var hours ??"
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)