when power transformer is flashed which gas is produce in
side?
Answers were Sorted based on User's Feedback
Answer / abbeer
Each of the fault result in thermal degradation of the oil
either alone or in combination with paper insulation. This
gives rise to the evaluation of various hydrocarbon gases,
hydrogen and oxides of carbon, in quantities depending on
the type of fault.
Heavy current arcing is characterized by the evolution of
significant quantities of hydrogen and acetylene (C2H2). If
the arcing also involves paper insulation, the oxide of
carbon will also be present.
Partial discharge usually results in evolution of hydrogen
and lower order hydrocarbons.
Localized heating or hot spot gives rise to methane and
ethane in appreciable amount.
Prolonged overloading or impaired heat transfer can cause
CO and CO2 to be generated due overheating paper
insulation.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / arunava
Hydrogen
O2
N2
Methane
CO
Ethane
CO2
Ethylene
Acetylene any of these.
Is This Answer Correct ? | 2 Yes | 6 No |
WHY CBCT USE ONLY IN Y PHASE NOT OTHER PHASES
Where earth point should provided in Ships or Submirines.
what is sevice settings for mccb?How can be it setted?
basic priniciple of induction motor
what is joule?
BRIEFELY EXPLAIN MEGGAR PRINCIPLE
What is BKW of Motor. And what its significance
what is RFID? thire application;
What is the difference between Derived earth Fault and measured earth fault.How it works.
if any house we instaled a 1.5 ton ac and its phase cable of wiring is installed but netrual cable of wiring not instaed. my question is that is neutual of house(for other wiring is capable for ac load or a sepeart neutrual wiring required
an amazing situation was faced when an alive distribution panel with 415 volts and carrying almost 200Amps has become short and this metal cubical showing 220 volts against neutral and earth. to redress any confusion i checked the panel with help of single 200watts test lamp which also glowing with max.intensity b/w neutral & metal body of DB. amazing situation is that i hold the DB firmly more than once with necked foot means without insulated shoes but not received any electrical shock. whereas our all running gen sets neutral points also proper grounded and this short DB was completely earthed , this is beyond my understanding . any body explain how is it possible . our running gen set neutral also grounded firmly
The Howland current source produces a A Unidirectional floating load current B Bidirectional single-ended load current C Unidirectional single-ended load current D Bidirectional floating load current