Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE
KNOW THAT LIGHTENING ARRESTER IS USED FOR OVER VOLTAGE
PROTECTION SO WHY NOT THE RATING OF LIGHTENING ARRESTER BE
MORE THAN 11KV ???????????????//

Answers were Sorted based on User's Feedback



RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED ..

Answer / elangovan t

Lightning arrester is to protect the system from any high
voltages such as lightning.
If the system voltage is 11kv, then the phase voltage will
be 11/sqrt(3)=6.35kv. It means the RMS voltage of the phase.
The maximum voltage or the peak voltage across the arrester
and earth will be 6.35*sqrt(2)=8.98kv.i.e 9kv.
Therefore, for 11kv line it is rated for 9kv.

Is This Answer Correct ?    135 Yes 10 No

RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED ..

Answer / h r jadhav

when we use ac line having system line voltage 11kv,in
this case phase voltage [phase to neutral which is earthed}
is 6.351 kv. lightening arrester is connected between phase
and neutral. lightening arester are nothing but the voltage
dependant resistors which act as insulator up to not only
the phase volatage ie 6.351 kv rms but ac peak voltage
reaches to 6.351 rms x root of 2 ie 1.414=8.98 kv. for
normal operation of system. thus the L A s are rated for
normal voltages 9 kv and discharge current generaly 10 kamp.
when ever voltage surges occures due to lightenig or either
by system abnormabilty,L A becomes for a instance as a
conductor provides path to surge voltages and prevents
failure of insulation leveles of equipment of system

Is This Answer Correct ?    32 Yes 5 No

RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED ..

Answer / nageshwar

FOR A 11KV LINE LINE TO GROUND VOLTAGE IS 11KV/SQRT(3). IT
GIVES OF THE ORDER OF 6KV ONLY. AS ARRESTER IS USED FOR
LINE TO GROUND TO DISCHARGE THE FAULT CURRENT TO GROUND ITS
RATING SHOULD BE MORE THAN 6KV. GENERALLY WE USE 9KV.

Is This Answer Correct ?    32 Yes 16 No

RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED ..

Answer / shirish

11kv is line voltage,but we put the lighting arrester in
phase so phase voltage of 11kv line is 6.351kv,now we can
not put rating of lighting arrester to 6.351kv because it is
normal phase voltage,so we put it 1.414(square root of
2)times more than phase voltage 6.6kv means 9kv.

Is This Answer Correct ?    13 Yes 4 No

RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED ..

Answer / gunasekaran

for solid grounding maximum voltage build up at earth faul
condition it self is not more than 80% of line voltage so
11*.8=8.8KV so we r using 9KV

Is This Answer Correct ?    8 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

specify the inbuilt protections in DG

0 Answers  


Why Closing coli supervision is not required for Circuit breaker.

1 Answers   JSW,


What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?

0 Answers   Eprosys Engineering Consultants,


what is first pole to clear factor

1 Answers  


why dimmerstate always connected in star connection? what will happen if it connected in delta?

0 Answers  


what is meant by servo motor ? how its operating either AC or DC?

0 Answers  


List out the different frequency domain specifications?

0 Answers  


How amny AH battery required for 600va inverter ?And how many hours it will give backup for ceiling fan ?

3 Answers   HCL,


Why corona leads to production of Ozone and glow of the color VOILET?

0 Answers  


what is the difference between concentrated winding and Distributed winding in motor?

7 Answers   BSL, Infosys, TCS,


WHAT INSTRUMENT IS USED TO MEASURE THE MAGNETIC FLUX?

7 Answers  


what type of relay has to be used for tripping the circuit from mains when a fault occur in a machine

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)