Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE
KNOW THAT LIGHTENING ARRESTER IS USED FOR OVER VOLTAGE
PROTECTION SO WHY NOT THE RATING OF LIGHTENING ARRESTER BE
MORE THAN 11KV ???????????????//

Answers were Sorted based on User's Feedback



RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED ..

Answer / elangovan t

Lightning arrester is to protect the system from any high
voltages such as lightning.
If the system voltage is 11kv, then the phase voltage will
be 11/sqrt(3)=6.35kv. It means the RMS voltage of the phase.
The maximum voltage or the peak voltage across the arrester
and earth will be 6.35*sqrt(2)=8.98kv.i.e 9kv.
Therefore, for 11kv line it is rated for 9kv.

Is This Answer Correct ?    135 Yes 10 No

RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED ..

Answer / h r jadhav

when we use ac line having system line voltage 11kv,in
this case phase voltage [phase to neutral which is earthed}
is 6.351 kv. lightening arrester is connected between phase
and neutral. lightening arester are nothing but the voltage
dependant resistors which act as insulator up to not only
the phase volatage ie 6.351 kv rms but ac peak voltage
reaches to 6.351 rms x root of 2 ie 1.414=8.98 kv. for
normal operation of system. thus the L A s are rated for
normal voltages 9 kv and discharge current generaly 10 kamp.
when ever voltage surges occures due to lightenig or either
by system abnormabilty,L A becomes for a instance as a
conductor provides path to surge voltages and prevents
failure of insulation leveles of equipment of system

Is This Answer Correct ?    32 Yes 5 No

RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED ..

Answer / nageshwar

FOR A 11KV LINE LINE TO GROUND VOLTAGE IS 11KV/SQRT(3). IT
GIVES OF THE ORDER OF 6KV ONLY. AS ARRESTER IS USED FOR
LINE TO GROUND TO DISCHARGE THE FAULT CURRENT TO GROUND ITS
RATING SHOULD BE MORE THAN 6KV. GENERALLY WE USE 9KV.

Is This Answer Correct ?    32 Yes 16 No

RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED ..

Answer / shirish

11kv is line voltage,but we put the lighting arrester in
phase so phase voltage of 11kv line is 6.351kv,now we can
not put rating of lighting arrester to 6.351kv because it is
normal phase voltage,so we put it 1.414(square root of
2)times more than phase voltage 6.6kv means 9kv.

Is This Answer Correct ?    13 Yes 4 No

RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE KNOW THAT LIGHTENING ARRESTER IS USED ..

Answer / gunasekaran

for solid grounding maximum voltage build up at earth faul
condition it self is not more than 80% of line voltage so
11*.8=8.8KV so we r using 9KV

Is This Answer Correct ?    8 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

Why are iron cores in transformers made laminated?

0 Answers  


Is it possible to implement Restricted Earth Fault protection for a transformer without neutral CT?

2 Answers  


why transformer tank is in rectangular shape what happen when it is in step shape

0 Answers  


Does magnetomonopoles exists? one maxwell equation strongly suggests no, but how about their existance in plasma?

0 Answers  


Differentiate between ideal and non ideal current sources?

0 Answers  


Transformer diagram mention each parts ?

0 Answers  


1. what is the meaning of bus? 2. what is the dc transformer? How it work 3.what is the function of the serge absorber? 4.How the CT and PT rating calculate/

1 Answers  


previous year paper of ntpc bhel for degree in electrical enng

0 Answers  


why field winding in synchronous machine connecting in star position?

1 Answers   HCL,


How to calulate cable size for 200KVA,160KVA& 40KVA load?

1 Answers   ABB,


What is the male and female contactors.where is it's used and what is the deferent betweens

1 Answers   Standard Chartered,


what is the function of anti pumping relays? what is KVAR? How it is generated in alternator? What is 3rd Harmonics? What is IDMT relay?

0 Answers   Aditya Birla,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)