RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV BUT WE
KNOW THAT LIGHTENING ARRESTER IS USED FOR OVER VOLTAGE
PROTECTION SO WHY NOT THE RATING OF LIGHTENING ARRESTER BE
MORE THAN 11KV ???????????????//
Answers were Sorted based on User's Feedback
Answer / elangovan t
Lightning arrester is to protect the system from any high
voltages such as lightning.
If the system voltage is 11kv, then the phase voltage will
be 11/sqrt(3)=6.35kv. It means the RMS voltage of the phase.
The maximum voltage or the peak voltage across the arrester
and earth will be 6.35*sqrt(2)=8.98kv.i.e 9kv.
Therefore, for 11kv line it is rated for 9kv.
| Is This Answer Correct ? | 135 Yes | 10 No |
Answer / h r jadhav
when we use ac line having system line voltage 11kv,in
this case phase voltage [phase to neutral which is earthed}
is 6.351 kv. lightening arrester is connected between phase
and neutral. lightening arester are nothing but the voltage
dependant resistors which act as insulator up to not only
the phase volatage ie 6.351 kv rms but ac peak voltage
reaches to 6.351 rms x root of 2 ie 1.414=8.98 kv. for
normal operation of system. thus the L A s are rated for
normal voltages 9 kv and discharge current generaly 10 kamp.
when ever voltage surges occures due to lightenig or either
by system abnormabilty,L A becomes for a instance as a
conductor provides path to surge voltages and prevents
failure of insulation leveles of equipment of system
| Is This Answer Correct ? | 32 Yes | 5 No |
Answer / nageshwar
FOR A 11KV LINE LINE TO GROUND VOLTAGE IS 11KV/SQRT(3). IT
GIVES OF THE ORDER OF 6KV ONLY. AS ARRESTER IS USED FOR
LINE TO GROUND TO DISCHARGE THE FAULT CURRENT TO GROUND ITS
RATING SHOULD BE MORE THAN 6KV. GENERALLY WE USE 9KV.
| Is This Answer Correct ? | 32 Yes | 16 No |
11kv is line voltage,but we put the lighting arrester in
phase so phase voltage of 11kv line is 6.351kv,now we can
not put rating of lighting arrester to 6.351kv because it is
normal phase voltage,so we put it 1.414(square root of
2)times more than phase voltage 6.6kv means 9kv.
| Is This Answer Correct ? | 13 Yes | 4 No |
Answer / gunasekaran
for solid grounding maximum voltage build up at earth faul
condition it self is not more than 80% of line voltage so
11*.8=8.8KV so we r using 9KV
| Is This Answer Correct ? | 8 Yes | 9 No |
why we connect the capacitor bank in star , not in delta in any system
What is the rating of your substation and what are the different types of substations?
Dear sir, How to calculate 3.5 core pvc aluminium armoured cable meter wise carrying amps rating.Please give the solution with a good example.
how much percentage set in transformer diffrencial relay
cost of operation of which plant is least?
how make to Incident and accident report
solar energy light efficiency & disadvantages?
How can I model an open-delta ground transformer for a network supplied by 4 unit GTG and power transformer in ETAP?
why three phase system is not preferred in aircrafts power cckts if yes than explain reasons?
What happen if 200KVAR capacitor continuesly connected to load and all the plant machinaries are not in working?
why rating of motor in HP ?
A 10 MVA, 66KV, 50Hz, Y-connected 3-phase alternator has synchronous reactance of 0.635 Ù. It is working at full load at 0.8 lagging p.f. condition. Find torque angle, neglect armature resistance.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)