1. how much normal earth resistance in earth pits(neutral
and body earth) and transformer neutral and body earth &
panel earth.
Answers were Sorted based on User's Feedback
Answer / rr0505
Earth resistance of earth pits shall depend on the terrain
in which the same is provided. Accordingly, based on soil
resistivity data of the location, no. of earth pits is
determined to ensure Grid earth resistance value below 5
Ohms for electrical grids,
For solidly grounded neutral of transformers, resistance
between Neutral & Body earth as well as panel earth shall
be zero.
| Is This Answer Correct ? | 124 Yes | 24 No |
Answer / rvg.msceb
The earthing resistance indicates the easiness of providing
a path. It should be as low as possible. Different
countries having standard values. In india, for commertial
applications its <1 ohm, and for railway its< 0.5 ohm.
for air craft and ships temp. earthing <10 ohm.etc.
| Is This Answer Correct ? | 82 Yes | 8 No |
Answer / shri6181
even any earth pit is concidered every earth pit should have the value 0ohms.but in rare cases u will get that value,more over will come 0.3to 0.9,there fore the earth pit value should be less than 1 ohm.ok
| Is This Answer Correct ? | 68 Yes | 9 No |
Answer / sanjay
NUETRAL&EARTH BETWEEN VALUE IS 0. AND TRANSFORMER BODY
EARTH AND NUETRAL BELOW 1OHM,ANDRESPECTIVELY PANEL EARTH
ISALSO BEBELOW 1OHM.
| Is This Answer Correct ? | 76 Yes | 38 No |
Answer / rakesh
For grid resitance it should be less than 5 ohms and for
indipendent earth pit it should less than 2 ohms.
| Is This Answer Correct ? | 51 Yes | 42 No |
Answer / kalpesh
earthing resetens 1 ohm to 3 ohm in rainy sesion only 1 ohm &other sesion aprox 3 ohm
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / kalpesh
Earth pit resistance 1.4 TO 1.6 NORMAL CNDITION
| Is This Answer Correct ? | 11 Yes | 6 No |
Answer / nandakumar.r
Earth pits resistance was 0 ohms.due to soil difference its
vary slightly near 2 ~ 3 ohms.But its acceptable level in
our country.
For transformer neutral and body earth and panel resisteance
was zero ohms.
| Is This Answer Correct ? | 13 Yes | 10 No |
Is there any calculation to find unknwon(unferroled) phases R Y B in alternator,3 phase motor anybody shoot my problem. how can we notice this is the respective phase?
what about SAP/MRP regarding manufacturing of electric motors and all drives?
how much resistence in proper earthing?
what is the difference between NC & CNC machine.what is the difference between equipment & machine tool
Period of infinite continuous fourier series a. N b. N+M c.infinite
12.5 KVAR capacitor 440V gas filled, Its used for windmill purpose, How can i know about microfarad value for this capacitor
The moisture in air will condense at
How do i calculate sizing of transformer on didstrubution load for high rise building.What should be MVA Rating of MV Panel feding by 122 kv.
can any one explain me the where is the use of plc and scada
why we do occ & scc test in transformer ?how we can do it ?
how we findout a ignater is faulty or not?
what is per unit calculation?looking for simple and strong explanation thk u
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)